Battery temperature sensor concern

CB
Chester Brummett
Sun, Jul 15, 2007 6:51 PM

Recent thread on battery temperature during charging relates to a problem that
I am experiencing.

Problem relates to charging from generator (or shore power).  Alternators when
running the engines use Balmar 612 regulators with attached battery and
alternator temperature sensors, and that system works good.

For generator or shore recharging, I have a Xantrex Prosine 3.0 and two each
40 amp TrueCharge chargers in parallel.  With full output, gives approx 200
amps charging.  I do see good load sharing with all three chargers on line.
Apparently the charge algorithm on all of these chargers is the same.

I don't want to get into another discussion on the "goodness" of the Xantrex
product line. If I was starting over, I would probably not use Xantrex, but it
is what I have, and I suspect that many list members also use Xantrex
products.

The chargers were installed with 3 separate temperature sensors on the battery
bank. The Prosine and TrueCharge threshold voltages with the temperature
sensors connected ("automatic mode") charges to 13.8 volts, and floats at 13.2
volts.  This 13.8 volt charge voltage does not adequately charge the
batteries, and results in an imbalance in measured specific gravity.  Any
attempt to equalize (overcharge) shuts down, voltage will not go over 13.8
volts.

Note same result with Prosine 3.0 only; the added parallel chargers do not
change the threshold.

Discussion with another boater, part time marine mechanic, who has installed a
number of Prosine 3.0.  His answer:  he has never been able to get the Prosine
to work properly with the battery temperature sensor attached.  His
recommendation:  unplug the sensor and "manually" set the temperature.  The
Prosine and TrueCharge have manual settings:  hot, warm, and cold for the
batteries.

When manually set to "warm" the chargers will charge to 14.2 - 14.3 volt
threshold, which I think is closer to desired.  After charging to this
threshold, the specific gravity does measure the same on all cells.

But, I am concerned about leaving the chargers without the battery temperature
sensors attached.  One possible partial solution:  a timer that starts each
time AC is applied to the chargers, and after two hours, trigger a relay to
"reconnect" the temperature sensor.  But this solution would still loose the
"protection" that the temperature sensor provides during high current charge,
when it is really needed.

Other information:  battery bank is 10 each Trojan T-145 batteries in
series-parallel, 1300 AH rated capacity.  I have not recorded engine room
temperature when the generator is running, I estimate 90 - 95 degrees.

Have others experienced similar issues when charging from the Prosine 3.0
and-or the TrueCharge 40?

Any advice on this concern will be appreciated.

Chet

Defever 44+5, Cygnet

Daytona Beach, FL

Recent thread on battery temperature during charging relates to a problem that I am experiencing. Problem relates to charging from generator (or shore power). Alternators when running the engines use Balmar 612 regulators with attached battery and alternator temperature sensors, and that system works good. For generator or shore recharging, I have a Xantrex Prosine 3.0 and two each 40 amp TrueCharge chargers in parallel. With full output, gives approx 200 amps charging. I do see good load sharing with all three chargers on line. Apparently the charge algorithm on all of these chargers is the same. I don't want to get into another discussion on the "goodness" of the Xantrex product line. If I was starting over, I would probably not use Xantrex, but it is what I have, and I suspect that many list members also use Xantrex products. The chargers were installed with 3 separate temperature sensors on the battery bank. The Prosine and TrueCharge threshold voltages with the temperature sensors connected ("automatic mode") charges to 13.8 volts, and floats at 13.2 volts. This 13.8 volt charge voltage does not adequately charge the batteries, and results in an imbalance in measured specific gravity. Any attempt to equalize (overcharge) shuts down, voltage will not go over 13.8 volts. Note same result with Prosine 3.0 only; the added parallel chargers do not change the threshold. Discussion with another boater, part time marine mechanic, who has installed a number of Prosine 3.0. His answer: he has never been able to get the Prosine to work properly with the battery temperature sensor attached. His recommendation: unplug the sensor and "manually" set the temperature. The Prosine and TrueCharge have manual settings: hot, warm, and cold for the batteries. When manually set to "warm" the chargers will charge to 14.2 - 14.3 volt threshold, which I think is closer to desired. After charging to this threshold, the specific gravity does measure the same on all cells. But, I am concerned about leaving the chargers without the battery temperature sensors attached. One possible partial solution: a timer that starts each time AC is applied to the chargers, and after two hours, trigger a relay to "reconnect" the temperature sensor. But this solution would still loose the "protection" that the temperature sensor provides during high current charge, when it is really needed. Other information: battery bank is 10 each Trojan T-145 batteries in series-parallel, 1300 AH rated capacity. I have not recorded engine room temperature when the generator is running, I estimate 90 - 95 degrees. Have others experienced similar issues when charging from the Prosine 3.0 and-or the TrueCharge 40? Any advice on this concern will be appreciated. Chet Defever 44+5, Cygnet Daytona Beach, FL
DS
Dan Stone
Sun, Jul 15, 2007 10:01 PM

-----Original Message-----
From: trawlers-and-trawlering-bounces@lists.samurai.com
[mailto:trawlers-and-trawlering-bounces@lists.samurai.com] On Behalf Of
Chester Brummett
Sent: Sunday, July 15, 2007 2:52 PM
To: trawlers-and-trawlering@lists.samurai.com
Subject: T&T: Battery temperature sensor concern

Recent thread on battery temperature during charging relates to a problem
that
I am experiencing.

Just one more idea into the mix....

Not exactly the same as your situation, but I very recently seem to have
solved a problem of a Xantrex 3-stage regulator, and then a similar Balmar
regulator, cutting back alternator output because of alternator overheating
(when IR temp readings didn't seem too hot).  Replaced the alternator temp
sensor and, with only a very few run hours, all seems right with the world.
The problem was a faulty temp sensor.  Balmar asked to have the sensor back
for "autopsy", since they "never" fail.

Dan Stone
M/V Slow Dance
Albin 43
St. Petersburg, FL

-----Original Message----- From: trawlers-and-trawlering-bounces@lists.samurai.com [mailto:trawlers-and-trawlering-bounces@lists.samurai.com] On Behalf Of Chester Brummett Sent: Sunday, July 15, 2007 2:52 PM To: trawlers-and-trawlering@lists.samurai.com Subject: T&T: Battery temperature sensor concern Recent thread on battery temperature during charging relates to a problem that I am experiencing. Just one more idea into the mix.... Not exactly the same as your situation, but I very recently seem to have solved a problem of a Xantrex 3-stage regulator, and then a similar Balmar regulator, cutting back alternator output because of alternator overheating (when IR temp readings didn't seem too hot). Replaced the alternator temp sensor and, with only a very few run hours, all seems right with the world. The problem was a faulty temp sensor. Balmar asked to have the sensor back for "autopsy", since they "never" fail. Dan Stone M/V Slow Dance Albin 43 St. Petersburg, FL
AW
Andy Woods
Tue, Jul 17, 2007 2:11 AM

Have others experienced similar issues when charging from the Prosine 3.0
and-or the TrueCharge 40?

I am running a Prosine 2.0 Inverter / Charger with 900 AH battery bank.  I
have a temperature sensor installed.  This charger gets well above 14 volts
when charging then backs down to 13.2 (I think) when in float.

Did this problem just appear or has it been a problem for a while?  If it
just appeared then I might suspect the temperature sensors.

Make sure your chargers are programmed properly for the battery type and amp
hours.  My book is on the boat but I know that by changing the program from
one battery manufacturer to another the voltages and charge rates might
change.  You might try programming for a generac battery of the type you
have.

Regards,

Andy

Andy Woods
Grand Folly
1970 Grand Banks 36 Classic
Georgetown, MD.
grandfolly@hotmail.com

>Have others experienced similar issues when charging from the Prosine 3.0 >and-or the TrueCharge 40? > I am running a Prosine 2.0 Inverter / Charger with 900 AH battery bank. I have a temperature sensor installed. This charger gets well above 14 volts when charging then backs down to 13.2 (I think) when in float. Did this problem just appear or has it been a problem for a while? If it just appeared then I might suspect the temperature sensors. Make sure your chargers are programmed properly for the battery type and amp hours. My book is on the boat but I know that by changing the program from one battery manufacturer to another the voltages and charge rates might change. You might try programming for a generac battery of the type you have. Regards, Andy Andy Woods Grand Folly 1970 Grand Banks 36 Classic Georgetown, MD. grandfolly@hotmail.com