time-nuts@lists.febo.com

Discussion of precise time and frequency measurement

View all threads

Daft idea with the National Grid

AT
Andy Talbot
Sun, Feb 7, 2021 9:24 PM

The UK has a standalone frequency locked grid supply, nominal 50Hz, which
typically wanders +/- about 0.15Hz RMS over several minutes , with
occasional short-lived excursions out to 0.2 or 0.3Hz.  Average number of
cycles per period generally is normalised to 50Hz after a few days.
The typical loading for the country ranges over ~25GW to 45GW

Now, I wonder:
I can probably measure the grid frequency to a few micro Hz  over a period
of tens of seconds. So I make a continuous recording of this, averaged over
say 10 second periods.
Now take a 7kW load (the maximum reasonably possible on a domestic circuit)
and switch it on and off at intervals of perhaps 10 minutes, precisely
timed so it can be correlated with the frequency log.  That 7kW load will
be about 0.2ppm of the average for that for the whole of the UK.    By post
processing, and some deep correlation covering days worth of cycles of load
on-off with the frequency, I wonder if it would be possible to see the
loading, the mean frequency changing by a few uHz.
Not sure what the time constant of the grid control is, but for* small
signals* I doubt it can be faster than a few minutes.

There was a serious outage on 9 August 2019 that caused frequency to drop
below 49.5Hz and initiate automatic load shedding;  that happened over a
period of a couple of minutes but was a large scale problem.
https://www.ofgem.gov.uk/publications-and-updates/investigation-9-august-2019-power-outage

Andy
www.g4jnt.com

The UK has a standalone frequency locked grid supply, nominal 50Hz, which typically wanders +/- about 0.15Hz RMS over several minutes , with occasional short-lived excursions out to 0.2 or 0.3Hz. Average number of cycles per period generally is normalised to 50Hz after a few days. The typical loading for the country ranges over ~25GW to 45GW Now, I wonder: I can probably measure the grid frequency to a few micro Hz over a period of tens of seconds. So I make a continuous recording of this, averaged over say 10 second periods. Now take a 7kW load (the maximum reasonably possible on a domestic circuit) and switch it on and off at intervals of perhaps 10 minutes, precisely timed so it can be correlated with the frequency log. That 7kW load will be about 0.2ppm of the average for that for the whole of the UK. By post processing, and some deep correlation covering days worth of cycles of load on-off with the frequency, I wonder if it would be possible to see the loading, the mean frequency changing by a few uHz. Not sure what the time constant of the grid control is, but for* small signals* I doubt it can be faster than a few minutes. There was a serious outage on 9 August 2019 that caused frequency to drop below 49.5Hz and initiate automatic load shedding; that happened over a period of a couple of minutes but was a large scale problem. https://www.ofgem.gov.uk/publications-and-updates/investigation-9-august-2019-power-outage Andy www.g4jnt.com
PG
Philip Gladstone
Sun, Feb 7, 2021 11:11 PM

As an amateur radio guy, I can't help wondering whether I could use this as
a very low bit rate channel across the country.

Philip

On Sun, Feb 7, 2021 at 4:44 PM Andy Talbot andy.g4jnt@gmail.com wrote:

The UK has a standalone frequency locked grid supply, nominal 50Hz, which
typically wanders +/- about 0.15Hz RMS over several minutes , with
occasional short-lived excursions out to 0.2 or 0.3Hz.  Average number of
cycles per period generally is normalised to 50Hz after a few days.
The typical loading for the country ranges over ~25GW to 45GW

Now, I wonder:
I can probably measure the grid frequency to a few micro Hz  over a period
of tens of seconds. So I make a continuous recording of this, averaged over
say 10 second periods.
Now take a 7kW load (the maximum reasonably possible on a domestic circuit)
and switch it on and off at intervals of perhaps 10 minutes, precisely
timed so it can be correlated with the frequency log.  That 7kW load will
be about 0.2ppm of the average for that for the whole of the UK.    By post
processing, and some deep correlation covering days worth of cycles of load
on-off with the frequency, I wonder if it would be possible to see the
loading, the mean frequency changing by a few uHz.
Not sure what the time constant of the grid control is, but for* small
signals* I doubt it can be faster than a few minutes.

There was a serious outage on 9 August 2019 that caused frequency to drop
below 49.5Hz and initiate automatic load shedding;  that happened over a
period of a couple of minutes but was a large scale problem.

https://www.ofgem.gov.uk/publications-and-updates/investigation-9-august-2019-power-outage

Andy
www.g4jnt.com


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to
http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
and follow the instructions there.

As an amateur radio guy, I can't help wondering whether I could use this as a *very* low bit rate channel across the country. Philip On Sun, Feb 7, 2021 at 4:44 PM Andy Talbot <andy.g4jnt@gmail.com> wrote: > The UK has a standalone frequency locked grid supply, nominal 50Hz, which > typically wanders +/- about 0.15Hz RMS over several minutes , with > occasional short-lived excursions out to 0.2 or 0.3Hz. Average number of > cycles per period generally is normalised to 50Hz after a few days. > The typical loading for the country ranges over ~25GW to 45GW > > Now, I wonder: > I can probably measure the grid frequency to a few micro Hz over a period > of tens of seconds. So I make a continuous recording of this, averaged over > say 10 second periods. > Now take a 7kW load (the maximum reasonably possible on a domestic circuit) > and switch it on and off at intervals of perhaps 10 minutes, precisely > timed so it can be correlated with the frequency log. That 7kW load will > be about 0.2ppm of the average for that for the whole of the UK. By post > processing, and some deep correlation covering days worth of cycles of load > on-off with the frequency, I wonder if it would be possible to see the > loading, the mean frequency changing by a few uHz. > Not sure what the time constant of the grid control is, but for* small > signals* I doubt it can be faster than a few minutes. > > There was a serious outage on 9 August 2019 that caused frequency to drop > below 49.5Hz and initiate automatic load shedding; that happened over a > period of a couple of minutes but was a large scale problem. > > https://www.ofgem.gov.uk/publications-and-updates/investigation-9-august-2019-power-outage > > Andy > www.g4jnt.com > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to > http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com > and follow the instructions there. >
DW
Dana Whitlow
Sun, Feb 7, 2021 11:28 PM

Not daft at all, Andy.  Closely related would be measurements of phase
change between
near the switched load and far away, over a stretch of a few system time
constants.
This would be more challenging, but perhaps doable.

Dana  K8YUM

On Sun, Feb 7, 2021 at 3:44 PM Andy Talbot andy.g4jnt@gmail.com wrote:

The UK has a standalone frequency locked grid supply, nominal 50Hz, which
typically wanders +/- about 0.15Hz RMS over several minutes , with
occasional short-lived excursions out to 0.2 or 0.3Hz.  Average number of
cycles per period generally is normalised to 50Hz after a few days.
The typical loading for the country ranges over ~25GW to 45GW

Now, I wonder:
I can probably measure the grid frequency to a few micro Hz  over a period
of tens of seconds. So I make a continuous recording of this, averaged over
say 10 second periods.
Now take a 7kW load (the maximum reasonably possible on a domestic circuit)
and switch it on and off at intervals of perhaps 10 minutes, precisely
timed so it can be correlated with the frequency log.  That 7kW load will
be about 0.2ppm of the average for that for the whole of the UK.    By post
processing, and some deep correlation covering days worth of cycles of load
on-off with the frequency, I wonder if it would be possible to see the
loading, the mean frequency changing by a few uHz.
Not sure what the time constant of the grid control is, but for* small
signals* I doubt it can be faster than a few minutes.

There was a serious outage on 9 August 2019 that caused frequency to drop
below 49.5Hz and initiate automatic load shedding;  that happened over a
period of a couple of minutes but was a large scale problem.

https://www.ofgem.gov.uk/publications-and-updates/investigation-9-august-2019-power-outage

Andy
www.g4jnt.com


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to
http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
and follow the instructions there.

Not daft at all, Andy. Closely related would be measurements of phase change between near the switched load and far away, over a stretch of a few system time constants. This would be more challenging, but perhaps doable. Dana K8YUM On Sun, Feb 7, 2021 at 3:44 PM Andy Talbot <andy.g4jnt@gmail.com> wrote: > The UK has a standalone frequency locked grid supply, nominal 50Hz, which > typically wanders +/- about 0.15Hz RMS over several minutes , with > occasional short-lived excursions out to 0.2 or 0.3Hz. Average number of > cycles per period generally is normalised to 50Hz after a few days. > The typical loading for the country ranges over ~25GW to 45GW > > Now, I wonder: > I can probably measure the grid frequency to a few micro Hz over a period > of tens of seconds. So I make a continuous recording of this, averaged over > say 10 second periods. > Now take a 7kW load (the maximum reasonably possible on a domestic circuit) > and switch it on and off at intervals of perhaps 10 minutes, precisely > timed so it can be correlated with the frequency log. That 7kW load will > be about 0.2ppm of the average for that for the whole of the UK. By post > processing, and some deep correlation covering days worth of cycles of load > on-off with the frequency, I wonder if it would be possible to see the > loading, the mean frequency changing by a few uHz. > Not sure what the time constant of the grid control is, but for* small > signals* I doubt it can be faster than a few minutes. > > There was a serious outage on 9 August 2019 that caused frequency to drop > below 49.5Hz and initiate automatic load shedding; that happened over a > period of a couple of minutes but was a large scale problem. > > https://www.ofgem.gov.uk/publications-and-updates/investigation-9-august-2019-power-outage > > Andy > www.g4jnt.com > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to > http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com > and follow the instructions there. >
GH
Gerhard Hoffmann
Mon, Feb 8, 2021 3:10 AM

Am 08.02.21 um 00:11 schrieb Philip Gladstone:

As an amateur radio guy, I can't help wondering whether I could use this as
a very low bit rate channel across the country.

I have done navigation for tv and phone sats, and the spread
navigation signals are just 20 dB under the MPEG data stream via
the analog transponder. If you back down another 10 or 20 dB, I'm
sure you could disseminate encryption keys or maybe phone without
anybody taking note. And everybody has a TV dish in the right direction.
Search the right one.
Really, I can't imagine that the agencies don't do that already.

Gerhard, DK4XP

Am 08.02.21 um 00:11 schrieb Philip Gladstone: > As an amateur radio guy, I can't help wondering whether I could use this as > a *very* low bit rate channel across the country. I have done navigation _for_ tv and phone sats, and the spread navigation signals are just 20 dB under the MPEG data stream via the analog transponder. If you back down another 10 or 20 dB, I'm sure you could disseminate encryption keys or maybe phone without anybody taking note. And everybody has a TV dish in the right direction. Search the right one. Really, I can't imagine that the agencies don't do that already. Gerhard, DK4XP
LJ
Lux, Jim
Mon, Feb 8, 2021 4:45 AM

On 2/7/21 3:28 PM, Dana Whitlow wrote:

Not daft at all, Andy.  Closely related would be measurements of phase
change between
near the switched load and far away, over a stretch of a few system time
constants.
This would be more challenging, but perhaps doable.

Dana  K8YUM

If you happen to own something like a steel mill running electric
furnaces or an aluminum refinery, so you can manipulate the load...

On 2/7/21 3:28 PM, Dana Whitlow wrote: > Not daft at all, Andy. Closely related would be measurements of phase > change between > near the switched load and far away, over a stretch of a few system time > constants. > This would be more challenging, but perhaps doable. > > Dana K8YUM > If you happen to own something like a steel mill running electric furnaces or an aluminum refinery, so you can manipulate the load...
PK
Poul-Henning Kamp
Mon, Feb 8, 2021 7:58 AM

Andy Talbot writes:

Not sure what the time constant of the grid control is, but for* small
signals* I doubt it can be faster than a few minutes.

There are generally spaking two time constants, the physical and the human.

The physical time constants are probably best understood as water in a
bucket:  If you kick it, complex ripples happen but eventually die out.

The timeconstant is generally order of five or ten cycles, unless you
make a short, those are much faster.

Mechanisms: Huge lumps of rotating iron, lots of switch-mode equipment
(including solar, wind mills and HVDC converters), magnetic hysteresis
in really big transformers, Maxwells/Telegraphers equations on long cables.

Unless the grid is on the verge of collapsing, the human time constant
is around 15 minutes.  Mechanism: People making mostly financial decisions.

As for your experiment, unless you use a psedurandom pattern, you stand
no chance of detecting a pattern.

I expect you may be able to show a bigger effect than you hypothesize
because the grid is not that "stiff".

Unless your house is right next to a big plant, there are five to ten
transformers between you and the power producer, and all of those "delay"
the phase in response to increasing load.

Your primary singal will therefore be phase-shift rather than frequency-
shift, which means your switching will have to be slow enough that
you can measure the difference between them.

PS: If you get friendly with people at grid control, they will send
you a copy of a pile of laplace equations from hell, which they use
to model the grid, and you can start by plugging your experiment
into them.  It wont be pretty.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

-------- Andy Talbot writes: > Not sure what the time constant of the grid control is, but for* small > signals* I doubt it can be faster than a few minutes. There are generally spaking two time constants, the physical and the human. The physical time constants are probably best understood as water in a bucket: If you kick it, complex ripples happen but eventually die out. The timeconstant is generally order of five or ten cycles, unless you make a short, those are much faster. Mechanisms: Huge lumps of rotating iron, lots of switch-mode equipment (including solar, wind mills and HVDC converters), magnetic hysteresis in really big transformers, Maxwells/Telegraphers equations on long cables. Unless the grid is on the verge of collapsing, the human time constant is around 15 minutes. Mechanism: People making mostly financial decisions. As for your experiment, unless you use a psedurandom pattern, you stand no chance of detecting a pattern. I expect you may be able to show a bigger effect than you hypothesize because the grid is not that "stiff". Unless your house is right next to a big plant, there are five to ten transformers between you and the power producer, and all of those "delay" the phase in response to increasing load. Your primary singal will therefore be phase-shift rather than frequency- shift, which means your switching will have to be slow enough that you can measure the difference between them. PS: If you get friendly with people at grid control, they will send you a copy of a pile of laplace equations from hell, which they use to model the grid, and you can start by plugging your experiment into them. It wont be pretty. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
PK
Poul-Henning Kamp
Mon, Feb 8, 2021 8:02 AM

Lux, Jim writes:

If you happen to own something like a steel mill running electric
furnaces or an aluminum refinery, so you can manipulate the load...

More scary:  Several independent studies have shown that even relatively
moderate bot-nets in the hands of somebody who knows the math of grid
stability would mean no grid stability.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

-------- Lux, Jim writes: > If you happen to own something like a steel mill running electric > furnaces or an aluminum refinery, so you can manipulate the load... More scary: Several independent studies have shown that even relatively moderate bot-nets in the hands of somebody who knows the math of grid stability would mean no grid stability. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
CJ
Clint Jay
Mon, Feb 8, 2021 11:45 AM

I'm not convinced they will be impressed by your scheme for ultra VLF
signalling Andy but it'd make a nice Radcom article

On Sun, 7 Feb 2021, 21:44 Andy Talbot, andy.g4jnt@gmail.com wrote:

The UK has a standalone frequency locked grid supply, nominal 50Hz, which
typically wanders +/- about 0.15Hz RMS over several minutes , with
occasional short-lived excursions out to 0.2 or 0.3Hz.  Average number of
cycles per period generally is normalised to 50Hz after a few days.
The typical loading for the country ranges over ~25GW to 45GW

Now, I wonder:
I can probably measure the grid frequency to a few micro Hz  over a period
of tens of seconds. So I make a continuous recording of this, averaged over
say 10 second periods.
Now take a 7kW load (the maximum reasonably possible on a domestic circuit)
and switch it on and off at intervals of perhaps 10 minutes, precisely
timed so it can be correlated with the frequency log.  That 7kW load will
be about 0.2ppm of the average for that for the whole of the UK.    By post
processing, and some deep correlation covering days worth of cycles of load
on-off with the frequency, I wonder if it would be possible to see the
loading, the mean frequency changing by a few uHz.
Not sure what the time constant of the grid control is, but for* small
signals* I doubt it can be faster than a few minutes.

There was a serious outage on 9 August 2019 that caused frequency to drop
below 49.5Hz and initiate automatic load shedding;  that happened over a
period of a couple of minutes but was a large scale problem.

https://www.ofgem.gov.uk/publications-and-updates/investigation-9-august-2019-power-outage

Andy
www.g4jnt.com


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to
http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
and follow the instructions there.

I'm not convinced they will be impressed by your scheme for ultra VLF signalling Andy but it'd make a nice Radcom article On Sun, 7 Feb 2021, 21:44 Andy Talbot, <andy.g4jnt@gmail.com> wrote: > The UK has a standalone frequency locked grid supply, nominal 50Hz, which > typically wanders +/- about 0.15Hz RMS over several minutes , with > occasional short-lived excursions out to 0.2 or 0.3Hz. Average number of > cycles per period generally is normalised to 50Hz after a few days. > The typical loading for the country ranges over ~25GW to 45GW > > Now, I wonder: > I can probably measure the grid frequency to a few micro Hz over a period > of tens of seconds. So I make a continuous recording of this, averaged over > say 10 second periods. > Now take a 7kW load (the maximum reasonably possible on a domestic circuit) > and switch it on and off at intervals of perhaps 10 minutes, precisely > timed so it can be correlated with the frequency log. That 7kW load will > be about 0.2ppm of the average for that for the whole of the UK. By post > processing, and some deep correlation covering days worth of cycles of load > on-off with the frequency, I wonder if it would be possible to see the > loading, the mean frequency changing by a few uHz. > Not sure what the time constant of the grid control is, but for* small > signals* I doubt it can be faster than a few minutes. > > There was a serious outage on 9 August 2019 that caused frequency to drop > below 49.5Hz and initiate automatic load shedding; that happened over a > period of a couple of minutes but was a large scale problem. > > https://www.ofgem.gov.uk/publications-and-updates/investigation-9-august-2019-power-outage > > Andy > www.g4jnt.com > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to > http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com > and follow the instructions there. >
LJ
Lux, Jim
Mon, Feb 8, 2021 2:48 PM

On 2/8/21 12:02 AM, Poul-Henning Kamp wrote:


Lux, Jim writes:

If you happen to own something like a steel mill running electric
furnaces or an aluminum refinery, so you can manipulate the load...

More scary:  Several independent studies have shown that even relatively
moderate bot-nets in the hands of somebody who knows the math of grid
stability would mean no grid stability.

This is a generalized concern with distributed generation (i.e. rooftop
solar panels on houses), because a bug in the controllers for the line
connected inverter could really screw things up. I suppose there's also
concerns about  malicious activity, but fiascos like the NEST
thermostats stopping  in winter of 2015/2016 are more likely.

On 2/8/21 12:02 AM, Poul-Henning Kamp wrote: > -------- > Lux, Jim writes: > >> If you happen to own something like a steel mill running electric >> furnaces or an aluminum refinery, so you can manipulate the load... > More scary: Several independent studies have shown that even relatively > moderate bot-nets in the hands of somebody who knows the math of grid > stability would mean no grid stability. > This is a generalized concern with distributed generation (i.e. rooftop solar panels on houses), because a bug in the controllers for the line connected inverter could really screw things up. I suppose there's also concerns about  malicious activity, but fiascos like the NEST thermostats stopping  in winter of 2015/2016 are more likely.
MS
Mark Spencer
Mon, Feb 8, 2021 7:46 PM

Years ago I recall reading accounts of efforts in the U.S. and perhaps Canada to track down the cause(s) of small but noticeable changes in the frequency of certain regional power grids that seemed to occur at more or less the same time each day.

Mark Spencer
mark@alignedsolutions.com
604 762 4099

On Feb 8, 2021, at 6:48 AM, Lux, Jim jim@luxfamily.com wrote:

On 2/8/21 12:02 AM, Poul-Henning Kamp wrote:

Lux, Jim writes:

If you happen to own something like a steel mill running electric
furnaces or an aluminum refinery, so you can manipulate the load...

More scary:  Several independent studies have shown that even relatively
moderate bot-nets in the hands of somebody who knows the math of grid
stability would mean no grid stability.

This is a generalized concern with distributed generation (i.e. rooftop solar panels on houses), because a bug in the controllers for the line connected inverter could really screw things up. I suppose there's also concerns about  malicious activity, but fiascos like the NEST thermostats stopping  in winter of 2015/2016 are more likely.


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
and follow the instructions there.

Years ago I recall reading accounts of efforts in the U.S. and perhaps Canada to track down the cause(s) of small but noticeable changes in the frequency of certain regional power grids that seemed to occur at more or less the same time each day. Mark Spencer mark@alignedsolutions.com 604 762 4099 > On Feb 8, 2021, at 6:48 AM, Lux, Jim <jim@luxfamily.com> wrote: > >> On 2/8/21 12:02 AM, Poul-Henning Kamp wrote: >> -------- >> Lux, Jim writes: >> >>> If you happen to own something like a steel mill running electric >>> furnaces or an aluminum refinery, so you can manipulate the load... >> More scary: Several independent studies have shown that even relatively >> moderate bot-nets in the hands of somebody who knows the math of grid >> stability would mean no grid stability. > This is a generalized concern with distributed generation (i.e. rooftop solar panels on houses), because a bug in the controllers for the line connected inverter could really screw things up. I suppose there's also concerns about malicious activity, but fiascos like the NEST thermostats stopping in winter of 2015/2016 are more likely. > > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com > and follow the instructions there.
J
joekokker@epios.eu
Mon, Feb 8, 2021 10:59 PM

Dear all,

it is quite an interesting premise. I think one of the challenges is to
even measure these small deviations in frequency. The time correlation
can be achieved with GNSS but the actual determination of the
zero-crossing might be the problem. I think the ZCD must be better than
100ns for this in each cycle. Local noise and environment conditions
render it quite difficult. When constructing a filter for the 50Hz, the
components must be very well designed to cope with the different
temperature, local noise and voltage amplitudes at two different places.

Regarding disruptions in the grid: there are various regulation
mechanisms. Generally the first 10-20 seconds physical effects stabilize
the grid. Afterwards the automatic control takes over.

  • saved rotational energy: an initial frequency drop due to a unexpected
    change in load or production is smoothed out by the inertia of all the
    generators, motors, pumps, etc. For a 10% mismatch in power without
    additional measures, the initial frequency drop would be about 1Hz per
    30 seconds.

  • self-regulation: a 1% drop in frequency leads to a ~2% reduction of
    load due to frequency dependent loads;

  • primary, automatic load-frequency control takes about 30 seconds to
    activate

After this rather short timescales, as Poul-Henning mentioned the human
factor (trading) has the biggest impacts on grid stability. It is
clearly visible with a periodicity of 15 minutes and more pronounced in
the evenings.

A small note on the recent frequency drop in the European grid:
https://www.entsoe.eu/news/2021/01/26/system-separation-in-the-continental-europe-synchronous-area-on-8-january-2021-2nd-update/

Best
Joe

On 2/8/21 8:46 PM, Mark Spencer wrote:

Years ago I recall reading accounts of efforts in the U.S. and perhaps Canada to track down the cause(s) of small but noticeable changes in the frequency of certain regional power grids that seemed to occur at more or less the same time each day.

Mark Spencer
mark@alignedsolutions.com
604 762 4099

On Feb 8, 2021, at 6:48 AM, Lux, Jim jim@luxfamily.com wrote:

On 2/8/21 12:02 AM, Poul-Henning Kamp wrote:

Lux, Jim writes:

If you happen to own something like a steel mill running electric
furnaces or an aluminum refinery, so you can manipulate the load...

More scary:  Several independent studies have shown that even relatively
moderate bot-nets in the hands of somebody who knows the math of grid
stability would mean no grid stability.

This is a generalized concern with distributed generation (i.e. rooftop solar panels on houses), because a bug in the controllers for the line connected inverter could really screw things up. I suppose there's also concerns about  malicious activity, but fiascos like the NEST thermostats stopping  in winter of 2015/2016 are more likely.


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
and follow the instructions there.


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
and follow the instructions there.

Dear all, it is quite an interesting premise. I think one of the challenges is to even measure these small deviations in frequency. The time correlation can be achieved with GNSS but the actual determination of the zero-crossing might be the problem. I think the ZCD must be better than 100ns for this in each cycle. Local noise and environment conditions render it quite difficult. When constructing a filter for the 50Hz, the components must be very well designed to cope with the different temperature, local noise and voltage amplitudes at two different places. Regarding disruptions in the grid: there are various regulation mechanisms. Generally the first 10-20 seconds physical effects stabilize the grid. Afterwards the automatic control takes over. - saved rotational energy: an initial frequency drop due to a unexpected change in load or production is smoothed out by the inertia of all the generators, motors, pumps, etc. For a 10% mismatch in power without additional measures, the initial frequency drop would be about 1Hz per 30 seconds. - self-regulation: a 1% drop in frequency leads to a ~2% reduction of load due to frequency dependent loads; - primary, automatic load-frequency control takes about 30 seconds to activate After this rather short timescales, as Poul-Henning mentioned the human factor (trading) has the biggest impacts on grid stability. It is clearly visible with a periodicity of 15 minutes and more pronounced in the evenings. A small note on the recent frequency drop in the European grid: https://www.entsoe.eu/news/2021/01/26/system-separation-in-the-continental-europe-synchronous-area-on-8-january-2021-2nd-update/ Best Joe On 2/8/21 8:46 PM, Mark Spencer wrote: > Years ago I recall reading accounts of efforts in the U.S. and perhaps Canada to track down the cause(s) of small but noticeable changes in the frequency of certain regional power grids that seemed to occur at more or less the same time each day. > > > Mark Spencer > mark@alignedsolutions.com > 604 762 4099 > >> On Feb 8, 2021, at 6:48 AM, Lux, Jim <jim@luxfamily.com> wrote: >> >>> On 2/8/21 12:02 AM, Poul-Henning Kamp wrote: >>> -------- >>> Lux, Jim writes: >>> >>>> If you happen to own something like a steel mill running electric >>>> furnaces or an aluminum refinery, so you can manipulate the load... >>> More scary: Several independent studies have shown that even relatively >>> moderate bot-nets in the hands of somebody who knows the math of grid >>> stability would mean no grid stability. >> This is a generalized concern with distributed generation (i.e. rooftop solar panels on houses), because a bug in the controllers for the line connected inverter could really screw things up. I suppose there's also concerns about malicious activity, but fiascos like the NEST thermostats stopping in winter of 2015/2016 are more likely. >> >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@lists.febo.com >> To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com >> and follow the instructions there. > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com > and follow the instructions there. >
DS
d.schuecker@avm.de
Tue, Feb 9, 2021 2:31 PM

Hi,

zero cross detection is not the best way to track grid frequency.
I built my grid frequency tracker with a uC sampling the grid at 160ks/s
and 12Bit. It is clocked by a TCXO. I fit a sine wave for every cycle of
the grid.

Fitting a sinewave is a linear problem, you do not need any approximations
and it is doable with a small uC. The samples of a sinewave are the
solution to the difference equation sig(n+1)=2*cos(w)*sig(n)-sig(n-1),
which is a linear equation for the unknown cos(w). That is straight and
simple linear algebra. I get a precision in the range of 4E-4 Hz.

Years ago I recall reading accounts of efforts in the U.S. and perhaps
Canada to track down the cause(s) of small but noticeable changes in the
frequency of certain regional power grids that seemed to occur at more or
less the same time each day.

In the european grid you have stable frequency changes in a 15min
timeframe, frequency being high in the morning and at night and low in the
afternoon. The 15 min timeframe is due to the 15min trade periode of the
European Energy Exchange trading platform located in Leipzig. The energy
brokers show a deterministic under/over-estimation of the european power
consumption which results in power shortage/surplus and thus frequency
rise or fall.

If I were a stock exchange geek I'd turn this information into money, much
money :))

Cheers
Detlef

"time-nuts" time-nuts-bounces@lists.febo.com schrieb am 08.02.2021
23:59:07:

Von: joekokker@epios.eu
An: time-nuts@lists.febo.com
Datum: 09.02.2021 00:05
Betreff: Re: [time-nuts] Daft idea with the National Grid
Gesendet von: "time-nuts" time-nuts-bounces@lists.febo.com

Dear all,

it is quite an interesting premise. I think one of the challenges is to
even measure these small deviations in frequency. The time correlation
can be achieved with GNSS but the actual determination of the
zero-crossing might be the problem. I think the ZCD must be better than
100ns for this in each cycle. Local noise and environment conditions
render it quite difficult. When constructing a filter for the 50Hz, the
components must be very well designed to cope with the different
temperature, local noise and voltage amplitudes at two different places.

Regarding disruptions in the grid: there are various regulation
mechanisms. Generally the first 10-20 seconds physical effects stabilize

the grid. Afterwards the automatic control takes over.

  • saved rotational energy: an initial frequency drop due to a unexpected

change in load or production is smoothed out by the inertia of all the
generators, motors, pumps, etc. For a 10% mismatch in power without
additional measures, the initial frequency drop would be about 1Hz per
30 seconds.

  • self-regulation: a 1% drop in frequency leads to a ~2% reduction of
    load due to frequency dependent loads;

  • primary, automatic load-frequency control takes about 30 seconds to
    activate

After this rather short timescales, as Poul-Henning mentioned the human
factor (trading) has the biggest impacts on grid stability. It is
clearly visible with a periodicity of 15 minutes and more pronounced in
the evenings.

A small note on the recent frequency drop in the European grid:
https://www.entsoe.eu/news/2021/01/26/system-separation-in-the-
continental-europe-synchronous-area-on-8-january-2021-2nd-update/

Best
Joe

On 2/8/21 8:46 PM, Mark Spencer wrote:

Years ago I recall reading accounts of efforts in the U.S. and

perhaps Canada to track down the cause(s) of small but noticeable
changes in the frequency of certain regional power grids that seemed
to occur at more or less the same time each day.

Mark Spencer
mark@alignedsolutions.com
604 762 4099

On Feb 8, 2021, at 6:48 AM, Lux, Jim jim@luxfamily.com wrote:

On 2/8/21 12:02 AM, Poul-Henning Kamp wrote:

Lux, Jim writes:

If you happen to own something like a steel mill running electric
furnaces or an aluminum refinery, so you can manipulate the load...

More scary:  Several independent studies have shown that even

relatively

moderate bot-nets in the hands of somebody who knows the math of

grid

stability would mean no grid stability.

This is a generalized concern with distributed generation (i.e.

rooftop solar panels on houses), because a bug in the controllers
for the line connected inverter could really screw things up. I
suppose there's also concerns about  malicious activity, but fiascos
like the NEST thermostats stopping  in winter of 2015/2016 are more

likely.


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to http://lists.febo.com/mailman/listinfo/

time-nuts_lists.febo.com

and follow the instructions there.


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time-

nuts_lists.febo.com

and follow the instructions there.


time-nuts mailing list -- time-nuts@lists.febo.com
To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time-
nuts_lists.febo.com
and follow the instructions there.

Hi, zero cross detection is not the best way to track grid frequency. I built my grid frequency tracker with a uC sampling the grid at 160ks/s and 12Bit. It is clocked by a TCXO. I fit a sine wave for every cycle of the grid. Fitting a sinewave is a linear problem, you do not need any approximations and it is doable with a small uC. The samples of a sinewave are the solution to the difference equation sig(n+1)=2*cos(w)*sig(n)-sig(n-1), which is a linear equation for the unknown cos(w). That is straight and simple linear algebra. I get a precision in the range of 4E-4 Hz. >>>>>>>>>>>>>>>>>>>>>> Years ago I recall reading accounts of efforts in the U.S. and perhaps Canada to track down the cause(s) of small but noticeable changes in the frequency of certain regional power grids that seemed to occur at more or less the same time each day. In the european grid you have stable frequency changes in a 15min timeframe, frequency being high in the morning and at night and low in the afternoon. The 15 min timeframe is due to the 15min trade periode of the European Energy Exchange trading platform located in Leipzig. The energy brokers show a deterministic under/over-estimation of the european power consumption which results in power shortage/surplus and thus frequency rise or fall. If I were a stock exchange geek I'd turn this information into money, much money :)) Cheers Detlef "time-nuts" <time-nuts-bounces@lists.febo.com> schrieb am 08.02.2021 23:59:07: > Von: joekokker@epios.eu > An: time-nuts@lists.febo.com > Datum: 09.02.2021 00:05 > Betreff: Re: [time-nuts] Daft idea with the National Grid > Gesendet von: "time-nuts" <time-nuts-bounces@lists.febo.com> > > Dear all, > > it is quite an interesting premise. I think one of the challenges is to > even measure these small deviations in frequency. The time correlation > can be achieved with GNSS but the actual determination of the > zero-crossing might be the problem. I think the ZCD must be better than > 100ns for this in each cycle. Local noise and environment conditions > render it quite difficult. When constructing a filter for the 50Hz, the > components must be very well designed to cope with the different > temperature, local noise and voltage amplitudes at two different places. > > Regarding disruptions in the grid: there are various regulation > mechanisms. Generally the first 10-20 seconds physical effects stabilize > the grid. Afterwards the automatic control takes over. > > - saved rotational energy: an initial frequency drop due to a unexpected > change in load or production is smoothed out by the inertia of all the > generators, motors, pumps, etc. For a 10% mismatch in power without > additional measures, the initial frequency drop would be about 1Hz per > 30 seconds. > > - self-regulation: a 1% drop in frequency leads to a ~2% reduction of > load due to frequency dependent loads; > > - primary, automatic load-frequency control takes about 30 seconds to > activate > > After this rather short timescales, as Poul-Henning mentioned the human > factor (trading) has the biggest impacts on grid stability. It is > clearly visible with a periodicity of 15 minutes and more pronounced in > the evenings. > > A small note on the recent frequency drop in the European grid: > https://www.entsoe.eu/news/2021/01/26/system-separation-in-the- > continental-europe-synchronous-area-on-8-january-2021-2nd-update/ > > Best > Joe > > On 2/8/21 8:46 PM, Mark Spencer wrote: > > Years ago I recall reading accounts of efforts in the U.S. and > perhaps Canada to track down the cause(s) of small but noticeable > changes in the frequency of certain regional power grids that seemed > to occur at more or less the same time each day. > > > > > > Mark Spencer > > mark@alignedsolutions.com > > 604 762 4099 > > > >> On Feb 8, 2021, at 6:48 AM, Lux, Jim <jim@luxfamily.com> wrote: > >> > >>> On 2/8/21 12:02 AM, Poul-Henning Kamp wrote: > >>> -------- > >>> Lux, Jim writes: > >>> > >>>> If you happen to own something like a steel mill running electric > >>>> furnaces or an aluminum refinery, so you can manipulate the load... > >>> More scary: Several independent studies have shown that even relatively > >>> moderate bot-nets in the hands of somebody who knows the math of grid > >>> stability would mean no grid stability. > >> This is a generalized concern with distributed generation (i.e. > rooftop solar panels on houses), because a bug in the controllers > for the line connected inverter could really screw things up. I > suppose there's also concerns about malicious activity, but fiascos > like the NEST thermostats stopping in winter of 2015/2016 are more likely. > >> > >> > >> _______________________________________________ > >> time-nuts mailing list -- time-nuts@lists.febo.com > >> To unsubscribe, go to http://lists.febo.com/mailman/listinfo/ > time-nuts_lists.febo.com > >> and follow the instructions there. > > > > _______________________________________________ > > time-nuts mailing list -- time-nuts@lists.febo.com > > To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time- > nuts_lists.febo.com > > and follow the instructions there. > > > > _______________________________________________ > time-nuts mailing list -- time-nuts@lists.febo.com > To unsubscribe, go to http://lists.febo.com/mailman/listinfo/time- > nuts_lists.febo.com > and follow the instructions there.