Mains frequency

BD
Bill Dailey
Tue, Nov 19, 2013 3:54 AM

ok Bob,

Then how do you tease out the difference between the clean generated 60Hz
and the mains 60Hz adev curves to determine what is noise and what is the
variability in the 60Hz?  That is the point of my question not semantics
about ideal vs non-ideal.

doc

On Mon, Nov 18, 2013 at 8:36 PM, Bob Camp lists@rtty.us wrote:

Hi

There is no way to come up with the noise floor of the picPET from that
plot. In fact coming up with the floor of a single channel device like the
picPET is not all that easy. First you need an ideal noise free sine wave
signal …. I’ve spent more than a few hours on that particular project with
other list members involved as well. As always we kept it off list to keep
from offending those who place a high value on their bandwidth.

Bob

On Nov 18, 2013, at 9:11 PM, Bill Dailey docdailey@gmail.com wrote:

I meant ideal at the noise floor of the picPET (i.e in this case the
generated 60Hz).

On Mon, Nov 18, 2013 at 8:08 PM, Bob Camp lists@rtty.us wrote:

Hi

An “ideal” curve would go to the bottom of the scale as soon as the plot
started. Anything that shows on the ADEV curve is by definition noise.

The

slope of the ADEV curve can help you determine what sort of noise it is.
The slope(s) on an modified ADEV curve can do that slightly better.

Bob

On Nov 18, 2013, at 8:03 PM, Bill Dailey docdailey@gmail.com wrote:

tom,

nice plots.  how do you figure out what the contribution of variability

vs

noise? In other words there is a differential between the "ideal" and

the

actual a dev curves... is there a way to tease out how much nose

contribute

to that differential?  It does seem to me that there should be far less
short term variability (< 100s) than there appears to be.  Clearly in

the

very short tau (< 0.1 s) the picPET can't tease that out but as the

curves

diverge, how much of that is noise? between say 0.1s and 100s?  Being a
power plant operator I would say quite a bit although I am rethinking

that

some due to the way the turbines push and pull each other.  I can

envision

some fine whole grid oscillations due to that push and pull.

bill

On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak tvb@leapsecond.com

wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd
like to see the results of the professional I-Q demodulated gear that

you

mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1

Msps

is going to reveal interesting amplitude and phase noise information.

But

see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is
fast enough to capture the zero-crossing of every 60 Hz cycle with 400

ns

resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the

picPET

though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply

from

the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set

to

9VAC at 60 Hz, a tentative noise floor measurement of the picPET when

used

this way.

My conclusions are that at least here in the US, or at least at my

house,

the short-term stability of mains hits about 5e-6, at about tau 0.2
seconds. The attached short-term plot is also not-inconsistent with

the

long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based

time-stamping

counter) is doing a pretty good job measuring this. Note, no software

or

data filtering was used. This is just raw serial/USB data going into
TimeLab.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO

ok Bob, Then how do you tease out the difference between the clean generated 60Hz and the mains 60Hz adev curves to determine what is noise and what is the variability in the 60Hz? That is the point of my question not semantics about ideal vs non-ideal. doc On Mon, Nov 18, 2013 at 8:36 PM, Bob Camp <lists@rtty.us> wrote: > Hi > > There is no way to come up with the noise floor of the picPET from that > plot. In fact coming up with the floor of a single channel device like the > picPET is not all that easy. First you need an ideal noise free sine wave > signal …. I’ve spent more than a few hours on that particular project with > other list members involved as well. As always we kept it off list to keep > from offending those who place a high value on their bandwidth. > > Bob > > On Nov 18, 2013, at 9:11 PM, Bill Dailey <docdailey@gmail.com> wrote: > > > I meant ideal at the noise floor of the picPET (i.e in this case the > > generated 60Hz). > > > > > > On Mon, Nov 18, 2013 at 8:08 PM, Bob Camp <lists@rtty.us> wrote: > > > >> Hi > >> > >> An “ideal” curve would go to the bottom of the scale as soon as the plot > >> started. Anything that shows on the ADEV curve is by definition noise. > The > >> slope of the ADEV curve can help you determine what sort of noise it is. > >> The slope(s) on an modified ADEV curve can do that slightly better. > >> > >> Bob > >> > >> On Nov 18, 2013, at 8:03 PM, Bill Dailey <docdailey@gmail.com> wrote: > >> > >>> tom, > >>> > >>> nice plots. how do you figure out what the contribution of variability > >> vs > >>> noise? In other words there is a differential between the "ideal" and > the > >>> actual a dev curves... is there a way to tease out how much nose > >> contribute > >>> to that differential? It does seem to me that there should be far less > >>> short term variability (< 100s) than there appears to be. Clearly in > the > >>> very short tau (< 0.1 s) the picPET can't tease that out but as the > >> curves > >>> diverge, how much of that is noise? between say 0.1s and 100s? Being a > >>> power plant operator I would say quite a bit although I am rethinking > >> that > >>> some due to the way the turbines push and pull each other. I can > >> envision > >>> some fine whole grid oscillations due to that push and pull. > >>> > >>> bill > >>> > >>> > >>> On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak <tvb@leapsecond.com> > >> wrote: > >>> > >>>> Magnus, > >>>> > >>>> I'm going to push back a bit on your mains sampling claim. Mostly, I'd > >>>> like to see the results of the professional I-Q demodulated gear that > >> you > >>>> mentioned. Can you post raw data, or a sample plot? > >>>> > >>>> I agree that looking at power line voltage with 16- or 24-bits at 1 > Msps > >>>> is going to reveal interesting amplitude and phase noise information. > >> But > >>>> see how well a $1 PIC can do. > >>>> > >>>> Attached is a plot made using TimeLab + picPET just now. The picPET is > >>>> fast enough to capture the zero-crossing of every 60 Hz cycle with 400 > >> ns > >>>> resolution; the TimeLab plots have tau0 of 16.67 ms. > >>>> > >>>> -- The blue trace was simply plugging a 9 VAC wall-wart into the > picPET > >>>> though a 10k resistor. > >>>> -- The pink trace was adding a 10 nF cap across the input. > >>>> -- The green trace was unplugging my laptop switching power supply > from > >>>> the same outlet! > >>>> -- The red trace is replacing the mains wall-wart with a hp 33120A set > >> to > >>>> 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when > >> used > >>>> this way. > >>>> > >>>> My conclusions are that at least here in the US, or at least at my > >> house, > >>>> the short-term stability of mains hits about 5e-6, at about tau 0.2 > >>>> seconds. The attached short-term plot is also not-inconsistent with > the > >>>> long-term plot at http://leapsecond.com/pages/mains/ > >>>> > >>>> My other conclusion is that the picPET (a simple PIC-based > time-stamping > >>>> counter) is doing a pretty good job measuring this. Note, no software > or > >>>> data filtering was used. This is just raw serial/USB data going into > >>>> TimeLab. > >>>> > >>>> /tvb > >>>> > >>>> _______________________________________________ > >>>> time-nuts mailing list -- time-nuts@febo.com > >>>> To unsubscribe, go to > >>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > >>>> and follow the instructions there. > >>>> > >>> > >>> > >>> > >>> -- > >>> Doc > >>> > >>> Bill Dailey > >>> KXØO > >>> _______________________________________________ > >>> time-nuts mailing list -- time-nuts@febo.com > >>> To unsubscribe, go to > >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > >>> and follow the instructions there. > >> > >> _______________________________________________ > >> time-nuts mailing list -- time-nuts@febo.com > >> To unsubscribe, go to > >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > >> and follow the instructions there. > >> > > > > > > > > -- > > Doc > > > > Bill Dailey > > KXØO > > _______________________________________________ > > time-nuts mailing list -- time-nuts@febo.com > > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > > and follow the instructions there. > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Doc Bill Dailey KXØO
TV
Tom Van Baak
Tue, Nov 19, 2013 11:06 AM

There is no way to come up with the noise floor of the picPET from that plot.

Hi Bob,

The goal of the red trace was to see if a fancy hp 33120A would give better or worse or same performance as mains 60 Hz. This simple substitution technique is a quick way to check if mains or the picPET might be the limiting factor. The slope and intercept suggests the picPET has resolution of at least 1e-6/tau. I say "at least" because we don't know how much of that is due to the 33120A.

Notice that for tau greater than about 1/3 second, picPET (and REF) instability is significantly below mains (DUT) instability. For tau 0.01 to 0.3 s it would take more work to quantify which pieces are contributing to the instability pie.

Attached is an ADEV plot; this one includes the past two weeks, and also a 100 day continuous run from Feb/Mar/Apr/May 2012. The GPSDO-like steering of mains frequency is visible in this trace.

You also might be wondering why the red trace hits a floor and drifts up. That's due to the TCXO in the 33120A. The reference for the picPET was one of those cute 10 MHz Micro-Crystal DIP OCXO, which easily outperforms the TCXO.

/tvb

> There is no way to come up with the noise floor of the picPET from that plot. Hi Bob, The goal of the red trace was to see if a fancy hp 33120A would give better or worse or same performance as mains 60 Hz. This simple substitution technique is a quick way to check if mains or the picPET might be the limiting factor. The slope and intercept suggests the picPET has resolution of at least 1e-6/tau. I say "at least" because we don't know how much of that is due to the 33120A. Notice that for tau greater than about 1/3 second, picPET (and REF) instability is significantly below mains (DUT) instability. For tau 0.01 to 0.3 s it would take more work to quantify which pieces are contributing to the instability pie. Attached is an ADEV plot; this one includes the past two weeks, and also a 100 day continuous run from Feb/Mar/Apr/May 2012. The GPSDO-like steering of mains frequency is visible in this trace. You also might be wondering why the red trace hits a floor and drifts up. That's due to the TCXO in the 33120A. The reference for the picPET was one of those cute 10 MHz Micro-Crystal DIP OCXO, which easily outperforms the TCXO. /tvb
PK
Poul-Henning Kamp
Tue, Nov 19, 2013 11:31 AM

In message 77A742979E2849FD9CA585192F2F5AFC@pc52, "Tom Van Baak" writes:

For tau 0.01 to 0.3 s it would take more work to quantify which pieces are
contributing to the instability pie.

It doesn't really make sense to talk about taus less than approx
0.1s for Mains.

It is not atypical to see 10% "harmonic distortion" on mains in a
household, most of it from switchmodes, but also single-phase
motors etc.  Music amplifiers, in particular played at "teenagerockgod"
volumes add a very interesting challenge too.

In theory harmonic distortion does not change your zero-crossings,
but it is not really "harmonic" in the Fourier sense, it's just
mostly centered around the overtones.

Either you include the "harmonic" distortion, and then your measurement
applies only to that specific outlet, when the dish-washer is running
exactly 20 minutes into programme 3 and no kids listen to loud
music.

Alternatively you can put mains through a 40-60 or 50-70 Hz
bandpassfilter to supress anything but the the fundamental, but
what exactly do you measure then ?

Once you get below about 1Hz, the most interesting thing you can
do with mains is to sample it at ~4kHz, make a water-fall plot and
try to identify your house-hold appliances by their distortion
patterns :-)

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

In message <77A742979E2849FD9CA585192F2F5AFC@pc52>, "Tom Van Baak" writes: >For tau 0.01 to 0.3 s it would take more work to quantify which pieces are >contributing to the instability pie. It doesn't really make sense to talk about taus less than approx 0.1s for Mains. It is not atypical to see 10% "harmonic distortion" on mains in a household, most of it from switchmodes, but also single-phase motors etc. Music amplifiers, in particular played at "teenagerockgod" volumes add a very interesting challenge too. In theory harmonic distortion does not change your zero-crossings, but it is not really "harmonic" in the Fourier sense, it's just mostly centered around the overtones. Either you include the "harmonic" distortion, and then your measurement applies only to that specific outlet, when the dish-washer is running exactly 20 minutes into programme 3 and no kids listen to loud music. Alternatively you can put mains through a 40-60 or 50-70 Hz bandpassfilter to supress anything but the the fundamental, but what exactly do you measure then ? Once you get below about 1Hz, the most interesting thing you can do with mains is to sample it at ~4kHz, make a water-fall plot and try to identify your house-hold appliances by their distortion patterns :-) -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
BC
Bob Camp
Tue, Nov 19, 2013 12:23 PM

Hi

I spent a lot of time with a sine wave input on this sort of stuff… You can come up with a line that the floor must be below. Find a better source and that line moves down. You can’t find the actual floor. You can only establish that it must be below this or that level. It’s not like the noise floor of a radio….

Bob

On Nov 19, 2013, at 6:06 AM, Tom Van Baak tvb@LeapSecond.com wrote:

There is no way to come up with the noise floor of the picPET from that plot.

Hi Bob,

The goal of the red trace was to see if a fancy hp 33120A would give better or worse or same performance as mains 60 Hz. This simple substitution technique is a quick way to check if mains or the picPET might be the limiting factor. The slope and intercept suggests the picPET has resolution of at least 1e-6/tau. I say "at least" because we don't know how much of that is due to the 33120A.

Notice that for tau greater than about 1/3 second, picPET (and REF) instability is significantly below mains (DUT) instability. For tau 0.01 to 0.3 s it would take more work to quantify which pieces are contributing to the instability pie.

Attached is an ADEV plot; this one includes the past two weeks, and also a 100 day continuous run from Feb/Mar/Apr/May 2012. The GPSDO-like steering of mains frequency is visible in this trace.

You also might be wondering why the red trace hits a floor and drifts up. That's due to the TCXO in the 33120A. The reference for the picPET was one of those cute 10 MHz Micro-Crystal DIP OCXO, which easily outperforms the TCXO.

/tvb
<mains-picpet-30.gif>_______________________________________________
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi I spent a lot of time with a sine wave input on this sort of stuff… You can come up with a line that the floor must be below. Find a better source and that line moves down. You can’t find the actual floor. You can only establish that it must be below this or that level. It’s not like the noise floor of a radio…. Bob On Nov 19, 2013, at 6:06 AM, Tom Van Baak <tvb@LeapSecond.com> wrote: >> There is no way to come up with the noise floor of the picPET from that plot. > > Hi Bob, > > The goal of the red trace was to see if a fancy hp 33120A would give better or worse or same performance as mains 60 Hz. This simple substitution technique is a quick way to check if mains or the picPET might be the limiting factor. The slope and intercept suggests the picPET has resolution of at least 1e-6/tau. I say "at least" because we don't know how much of that is due to the 33120A. > > Notice that for tau greater than about 1/3 second, picPET (and REF) instability is significantly below mains (DUT) instability. For tau 0.01 to 0.3 s it would take more work to quantify which pieces are contributing to the instability pie. > > Attached is an ADEV plot; this one includes the past two weeks, and also a 100 day continuous run from Feb/Mar/Apr/May 2012. The GPSDO-like steering of mains frequency is visible in this trace. > > You also might be wondering why the red trace hits a floor and drifts up. That's due to the TCXO in the 33120A. The reference for the picPET was one of those cute 10 MHz Micro-Crystal DIP OCXO, which easily outperforms the TCXO. > > /tvb > <mains-picpet-30.gif>_______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BC
Bob Camp
Tue, Nov 19, 2013 12:26 PM

HI

There is no way to tell that the “clean” 60 Hz is actually clean. It’s got a noise component in it. The noise actually is surprisingly high. The picPET is actually a bit better than that plot would suggest.  You can say that the noise of the picPET is below the “clean” line and move on, but that’s not the whole story.

Bob

On Nov 18, 2013, at 10:54 PM, Bill Dailey docdailey@gmail.com wrote:

ok Bob,

Then how do you tease out the difference between the clean generated 60Hz
and the mains 60Hz adev curves to determine what is noise and what is the
variability in the 60Hz?  That is the point of my question not semantics
about ideal vs non-ideal.

doc

On Mon, Nov 18, 2013 at 8:36 PM, Bob Camp lists@rtty.us wrote:

Hi

There is no way to come up with the noise floor of the picPET from that
plot. In fact coming up with the floor of a single channel device like the
picPET is not all that easy. First you need an ideal noise free sine wave
signal …. I’ve spent more than a few hours on that particular project with
other list members involved as well. As always we kept it off list to keep
from offending those who place a high value on their bandwidth.

Bob

On Nov 18, 2013, at 9:11 PM, Bill Dailey docdailey@gmail.com wrote:

I meant ideal at the noise floor of the picPET (i.e in this case the
generated 60Hz).

On Mon, Nov 18, 2013 at 8:08 PM, Bob Camp lists@rtty.us wrote:

Hi

An “ideal” curve would go to the bottom of the scale as soon as the plot
started. Anything that shows on the ADEV curve is by definition noise.

The

slope of the ADEV curve can help you determine what sort of noise it is.
The slope(s) on an modified ADEV curve can do that slightly better.

Bob

On Nov 18, 2013, at 8:03 PM, Bill Dailey docdailey@gmail.com wrote:

tom,

nice plots.  how do you figure out what the contribution of variability

vs

noise? In other words there is a differential between the "ideal" and

the

actual a dev curves... is there a way to tease out how much nose

contribute

to that differential?  It does seem to me that there should be far less
short term variability (< 100s) than there appears to be.  Clearly in

the

very short tau (< 0.1 s) the picPET can't tease that out but as the

curves

diverge, how much of that is noise? between say 0.1s and 100s?  Being a
power plant operator I would say quite a bit although I am rethinking

that

some due to the way the turbines push and pull each other.  I can

envision

some fine whole grid oscillations due to that push and pull.

bill

On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak tvb@leapsecond.com

wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd
like to see the results of the professional I-Q demodulated gear that

you

mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1

Msps

is going to reveal interesting amplitude and phase noise information.

But

see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is
fast enough to capture the zero-crossing of every 60 Hz cycle with 400

ns

resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the

picPET

though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply

from

the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set

to

9VAC at 60 Hz, a tentative noise floor measurement of the picPET when

used

this way.

My conclusions are that at least here in the US, or at least at my

house,

the short-term stability of mains hits about 5e-6, at about tau 0.2
seconds. The attached short-term plot is also not-inconsistent with

the

long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based

time-stamping

counter) is doing a pretty good job measuring this. Note, no software

or

data filtering was used. This is just raw serial/USB data going into
TimeLab.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

HI There is no way to tell that the “clean” 60 Hz is actually clean. It’s got a noise component in it. The noise actually is surprisingly high. The picPET is actually a bit better than that plot would suggest. You can say that the noise of the picPET is below the “clean” line and move on, but that’s not the whole story. Bob On Nov 18, 2013, at 10:54 PM, Bill Dailey <docdailey@gmail.com> wrote: > ok Bob, > > Then how do you tease out the difference between the clean generated 60Hz > and the mains 60Hz adev curves to determine what is noise and what is the > variability in the 60Hz? That is the point of my question not semantics > about ideal vs non-ideal. > > doc > > > On Mon, Nov 18, 2013 at 8:36 PM, Bob Camp <lists@rtty.us> wrote: > >> Hi >> >> There is no way to come up with the noise floor of the picPET from that >> plot. In fact coming up with the floor of a single channel device like the >> picPET is not all that easy. First you need an ideal noise free sine wave >> signal …. I’ve spent more than a few hours on that particular project with >> other list members involved as well. As always we kept it off list to keep >> from offending those who place a high value on their bandwidth. >> >> Bob >> >> On Nov 18, 2013, at 9:11 PM, Bill Dailey <docdailey@gmail.com> wrote: >> >>> I meant ideal at the noise floor of the picPET (i.e in this case the >>> generated 60Hz). >>> >>> >>> On Mon, Nov 18, 2013 at 8:08 PM, Bob Camp <lists@rtty.us> wrote: >>> >>>> Hi >>>> >>>> An “ideal” curve would go to the bottom of the scale as soon as the plot >>>> started. Anything that shows on the ADEV curve is by definition noise. >> The >>>> slope of the ADEV curve can help you determine what sort of noise it is. >>>> The slope(s) on an modified ADEV curve can do that slightly better. >>>> >>>> Bob >>>> >>>> On Nov 18, 2013, at 8:03 PM, Bill Dailey <docdailey@gmail.com> wrote: >>>> >>>>> tom, >>>>> >>>>> nice plots. how do you figure out what the contribution of variability >>>> vs >>>>> noise? In other words there is a differential between the "ideal" and >> the >>>>> actual a dev curves... is there a way to tease out how much nose >>>> contribute >>>>> to that differential? It does seem to me that there should be far less >>>>> short term variability (< 100s) than there appears to be. Clearly in >> the >>>>> very short tau (< 0.1 s) the picPET can't tease that out but as the >>>> curves >>>>> diverge, how much of that is noise? between say 0.1s and 100s? Being a >>>>> power plant operator I would say quite a bit although I am rethinking >>>> that >>>>> some due to the way the turbines push and pull each other. I can >>>> envision >>>>> some fine whole grid oscillations due to that push and pull. >>>>> >>>>> bill >>>>> >>>>> >>>>> On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak <tvb@leapsecond.com> >>>> wrote: >>>>> >>>>>> Magnus, >>>>>> >>>>>> I'm going to push back a bit on your mains sampling claim. Mostly, I'd >>>>>> like to see the results of the professional I-Q demodulated gear that >>>> you >>>>>> mentioned. Can you post raw data, or a sample plot? >>>>>> >>>>>> I agree that looking at power line voltage with 16- or 24-bits at 1 >> Msps >>>>>> is going to reveal interesting amplitude and phase noise information. >>>> But >>>>>> see how well a $1 PIC can do. >>>>>> >>>>>> Attached is a plot made using TimeLab + picPET just now. The picPET is >>>>>> fast enough to capture the zero-crossing of every 60 Hz cycle with 400 >>>> ns >>>>>> resolution; the TimeLab plots have tau0 of 16.67 ms. >>>>>> >>>>>> -- The blue trace was simply plugging a 9 VAC wall-wart into the >> picPET >>>>>> though a 10k resistor. >>>>>> -- The pink trace was adding a 10 nF cap across the input. >>>>>> -- The green trace was unplugging my laptop switching power supply >> from >>>>>> the same outlet! >>>>>> -- The red trace is replacing the mains wall-wart with a hp 33120A set >>>> to >>>>>> 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when >>>> used >>>>>> this way. >>>>>> >>>>>> My conclusions are that at least here in the US, or at least at my >>>> house, >>>>>> the short-term stability of mains hits about 5e-6, at about tau 0.2 >>>>>> seconds. The attached short-term plot is also not-inconsistent with >> the >>>>>> long-term plot at http://leapsecond.com/pages/mains/ >>>>>> >>>>>> My other conclusion is that the picPET (a simple PIC-based >> time-stamping >>>>>> counter) is doing a pretty good job measuring this. Note, no software >> or >>>>>> data filtering was used. This is just raw serial/USB data going into >>>>>> TimeLab. >>>>>> >>>>>> /tvb >>>>>> >>>>>> _______________________________________________ >>>>>> time-nuts mailing list -- time-nuts@febo.com >>>>>> To unsubscribe, go to >>>>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>>>> and follow the instructions there. >>>>>> >>>>> >>>>> >>>>> >>>>> -- >>>>> Doc >>>>> >>>>> Bill Dailey >>>>> KXØO >>>>> _______________________________________________ >>>>> time-nuts mailing list -- time-nuts@febo.com >>>>> To unsubscribe, go to >>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>>> and follow the instructions there. >>>> >>>> _______________________________________________ >>>> time-nuts mailing list -- time-nuts@febo.com >>>> To unsubscribe, go to >>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>> and follow the instructions there. >>>> >>> >>> >>> >>> -- >>> Doc >>> >>> Bill Dailey >>> KXØO >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > > > > -- > Doc > > Bill Dailey > KXØO > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
DM
Daniel Mendes
Tue, Nov 19, 2013 1:44 PM

Em 19/11/2013 09:31, Poul-Henning Kamp escreveu:

In theory harmonic distortion does not change your zero-crossings,

The odd ones doesn´t, but the even ones do... and they happen.

Daniel

Em 19/11/2013 09:31, Poul-Henning Kamp escreveu: > In theory harmonic distortion does not change your zero-crossings, The odd ones doesn´t, but the even ones do... and they happen. Daniel
DJ
Didier Juges
Tue, Nov 19, 2013 3:06 PM

"Alternatively you can put mains through a 40-60 or 50-70 Hz
bandpass filter to suppress anything but the fundamental"

The problem with any filtering is precisely that the phase shift through any filter is highly dependent on the actual signal frequency, so if your purpose is timing, the filter will probably do more damage than help. Tom's data shows that "no filter" works well at his location, which is probably typical, aside from the large number of precision time references in the basement :)

I have some data about filtering the mains I am trying to put together in a web page. Will take a few days. That data was collected with regard to power factor correction, not timing, but it is within the scope of what has been discussed in this thread and it may be interesting to the curious mind.

Didier KO4BB

Poul-Henning Kamp phk@phk.freebsd.dk wrote:

In message 77A742979E2849FD9CA585192F2F5AFC@pc52, "Tom Van Baak"
writes:

For tau 0.01 to 0.3 s it would take more work to quantify which pieces

are

contributing to the instability pie.

It doesn't really make sense to talk about taus less than approx
0.1s for Mains.

It is not atypical to see 10% "harmonic distortion" on mains in a
household, most of it from switchmodes, but also single-phase
motors etc.  Music amplifiers, in particular played at "teenagerockgod"
volumes add a very interesting challenge too.

In theory harmonic distortion does not change your zero-crossings,
but it is not really "harmonic" in the Fourier sense, it's just
mostly centered around the overtones.

Either you include the "harmonic" distortion, and then your measurement
applies only to that specific outlet, when the dish-washer is running
exactly 20 minutes into programme 3 and no kids listen to loud
music.

Alternatively you can put mains through a 40-60 or 50-70 Hz
bandpassfilter to supress anything but the the fundamental, but
what exactly do you measure then ?

Once you get below about 1Hz, the most interesting thing you can
do with mains is to sample it at ~4kHz, make a water-fall plot and
try to identify your house-hold appliances by their distortion
patterns :-)

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by
incompetence.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other things.

"Alternatively you can put mains through a 40-60 or 50-70 Hz bandpass filter to suppress anything but the fundamental" The problem with any filtering is precisely that the phase shift through any filter is highly dependent on the actual signal frequency, so if your purpose is timing, the filter will probably do more damage than help. Tom's data shows that "no filter" works well at his location, which is probably typical, aside from the large number of precision time references in the basement :) I have some data about filtering the mains I am trying to put together in a web page. Will take a few days. That data was collected with regard to power factor correction, not timing, but it is within the scope of what has been discussed in this thread and it may be interesting to the curious mind. Didier KO4BB Poul-Henning Kamp <phk@phk.freebsd.dk> wrote: >In message <77A742979E2849FD9CA585192F2F5AFC@pc52>, "Tom Van Baak" >writes: > >>For tau 0.01 to 0.3 s it would take more work to quantify which pieces >are >>contributing to the instability pie. > >It doesn't really make sense to talk about taus less than approx >0.1s for Mains. > >It is not atypical to see 10% "harmonic distortion" on mains in a >household, most of it from switchmodes, but also single-phase >motors etc. Music amplifiers, in particular played at "teenagerockgod" >volumes add a very interesting challenge too. > >In theory harmonic distortion does not change your zero-crossings, >but it is not really "harmonic" in the Fourier sense, it's just >mostly centered around the overtones. > >Either you include the "harmonic" distortion, and then your measurement >applies only to that specific outlet, when the dish-washer is running >exactly 20 minutes into programme 3 and no kids listen to loud >music. > >Alternatively you can put mains through a 40-60 or 50-70 Hz >bandpassfilter to supress anything but the the fundamental, but >what exactly do you measure then ? > >Once you get below about 1Hz, the most interesting thing you can >do with mains is to sample it at ~4kHz, make a water-fall plot and >try to identify your house-hold appliances by their distortion >patterns :-) > >-- >Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 >phk@FreeBSD.ORG | TCP/IP since RFC 956 >FreeBSD committer | BSD since 4.3-tahoe >Never attribute to malice what can adequately be explained by >incompetence. >_______________________________________________ >time-nuts mailing list -- time-nuts@febo.com >To unsubscribe, go to >https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >and follow the instructions there. -- Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other things.
TS
Tim Shoppa
Tue, Nov 19, 2013 4:54 PM

Filter families that aim for super flat passbands and super steep skirts
have the craziest phase response. They also "ring like a bell" when hit
with impulses.

Other filter families aim for well controlled phase response but give up
flat passbands and super steep skirts. They do not "ring like a bell" when
hit with impulses.

Gaussian filters work very well for well controlled phase response and are
used in e.g. oscilliscopes and other applications where the data is eyed
critically in the time domain.

In communications and time-domain work, it is common to use a filter that
has well controlled phase delay across the passband, but still has somewhat
steep skirts and can have less well controlled phase delay outside the
passband. In the literature these are called "Gaussian to 12dB" and
similar. They are a joy to listen with, in environments with impulse noise,
compared to the typical steep-skirt filters.

Tim N3QE

Tim.

On Tue, Nov 19, 2013 at 10:06 AM, Didier Juges shalimr9@gmail.com wrote:

"Alternatively you can put mains through a 40-60 or 50-70 Hz
bandpass filter to suppress anything but the fundamental"

The problem with any filtering is precisely that the phase shift through
any filter is highly dependent on the actual signal frequency, so if your
purpose is timing, the filter will probably do more damage than help. Tom's
data shows that "no filter" works well at his location, which is probably
typical, aside from the large number of precision time references in the
basement :)

I have some data about filtering the mains I am trying to put together in
a web page. Will take a few days. That data was collected with regard to
power factor correction, not timing, but it is within the scope of what has
been discussed in this thread and it may be interesting to the curious mind.

Didier KO4BB

Poul-Henning Kamp phk@phk.freebsd.dk wrote:

In message 77A742979E2849FD9CA585192F2F5AFC@pc52, "Tom Van Baak"
writes:

For tau 0.01 to 0.3 s it would take more work to quantify which pieces

are

contributing to the instability pie.

It doesn't really make sense to talk about taus less than approx
0.1s for Mains.

It is not atypical to see 10% "harmonic distortion" on mains in a
household, most of it from switchmodes, but also single-phase
motors etc.  Music amplifiers, in particular played at "teenagerockgod"
volumes add a very interesting challenge too.

In theory harmonic distortion does not change your zero-crossings,
but it is not really "harmonic" in the Fourier sense, it's just
mostly centered around the overtones.

Either you include the "harmonic" distortion, and then your measurement
applies only to that specific outlet, when the dish-washer is running
exactly 20 minutes into programme 3 and no kids listen to loud
music.

Alternatively you can put mains through a 40-60 or 50-70 Hz
bandpassfilter to supress anything but the the fundamental, but
what exactly do you measure then ?

Once you get below about 1Hz, the most interesting thing you can
do with mains is to sample it at ~4kHz, make a water-fall plot and
try to identify your house-hold appliances by their distortion
patterns :-)

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by
incompetence.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other
things.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Filter families that aim for super flat passbands and super steep skirts have the craziest phase response. They also "ring like a bell" when hit with impulses. Other filter families aim for well controlled phase response but give up flat passbands and super steep skirts. They do not "ring like a bell" when hit with impulses. Gaussian filters work very well for well controlled phase response and are used in e.g. oscilliscopes and other applications where the data is eyed critically in the time domain. In communications and time-domain work, it is common to use a filter that has well controlled phase delay across the passband, but still has somewhat steep skirts and can have less well controlled phase delay outside the passband. In the literature these are called "Gaussian to 12dB" and similar. They are a joy to listen with, in environments with impulse noise, compared to the typical steep-skirt filters. Tim N3QE Tim. On Tue, Nov 19, 2013 at 10:06 AM, Didier Juges <shalimr9@gmail.com> wrote: > "Alternatively you can put mains through a 40-60 or 50-70 Hz > bandpass filter to suppress anything but the fundamental" > > The problem with any filtering is precisely that the phase shift through > any filter is highly dependent on the actual signal frequency, so if your > purpose is timing, the filter will probably do more damage than help. Tom's > data shows that "no filter" works well at his location, which is probably > typical, aside from the large number of precision time references in the > basement :) > > I have some data about filtering the mains I am trying to put together in > a web page. Will take a few days. That data was collected with regard to > power factor correction, not timing, but it is within the scope of what has > been discussed in this thread and it may be interesting to the curious mind. > > Didier KO4BB > > > Poul-Henning Kamp <phk@phk.freebsd.dk> wrote: > >In message <77A742979E2849FD9CA585192F2F5AFC@pc52>, "Tom Van Baak" > >writes: > > > >>For tau 0.01 to 0.3 s it would take more work to quantify which pieces > >are > >>contributing to the instability pie. > > > >It doesn't really make sense to talk about taus less than approx > >0.1s for Mains. > > > >It is not atypical to see 10% "harmonic distortion" on mains in a > >household, most of it from switchmodes, but also single-phase > >motors etc. Music amplifiers, in particular played at "teenagerockgod" > >volumes add a very interesting challenge too. > > > >In theory harmonic distortion does not change your zero-crossings, > >but it is not really "harmonic" in the Fourier sense, it's just > >mostly centered around the overtones. > > > >Either you include the "harmonic" distortion, and then your measurement > >applies only to that specific outlet, when the dish-washer is running > >exactly 20 minutes into programme 3 and no kids listen to loud > >music. > > > >Alternatively you can put mains through a 40-60 or 50-70 Hz > >bandpassfilter to supress anything but the the fundamental, but > >what exactly do you measure then ? > > > >Once you get below about 1Hz, the most interesting thing you can > >do with mains is to sample it at ~4kHz, make a water-fall plot and > >try to identify your house-hold appliances by their distortion > >patterns :-) > > > >-- > >Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 > >phk@FreeBSD.ORG | TCP/IP since RFC 956 > >FreeBSD committer | BSD since 4.3-tahoe > >Never attribute to malice what can adequately be explained by > >incompetence. > >_______________________________________________ > >time-nuts mailing list -- time-nuts@febo.com > >To unsubscribe, go to > >https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > >and follow the instructions there. > > -- > Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other > things. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
MD
Magnus Danielson
Wed, Mar 12, 2014 3:39 PM

Tom,

On 18/11/13 23:15, Tom Van Baak wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot?

I don't have much of that myself. I do recommend you to check the
presentations of the NASPI conference (naspi.org). There is plenty of
plots there.

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do.

Well, I should toss that over to the good folk at NIST doing
synchrophasor calibrations. Should I grab them now that we are in the
same room?

Have a look at IEEE C37.118.1 for measurement methods.

Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way.

My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab.

Well, if you are happy with that, fine. But there are many things
happening on the grid which needs deep analysis and the tools for it has
been developed to provide both resolution and removal of noise which is
not part of the measurments. Just calibrating the trigger noise for a
PMU requires care, as the S/N required for a straight comparator for the
applications is several tens of dBs away from a good conditions, so they
have had issues with doing that.

Doing your own time-stamping like you have done is naturally fun, but do
not confuse it with the experience and processing that have been shown
needed by an industry.

BTW. WECC, who has a large network of PMUs, and that covers where you
have your house and measurement point, can't release detailed data to me
or you just for fun. It always needs to be cleared from a security point
of view.

Cheers,
Magnus

Tom, On 18/11/13 23:15, Tom Van Baak wrote: > Magnus, > > I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot? I don't have much of that myself. I do recommend you to check the presentations of the NASPI conference (naspi.org). There is plenty of plots there. > I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do. Well, I should toss that over to the good folk at NIST doing synchrophasor calibrations. Should I grab them now that we are in the same room? Have a look at IEEE C37.118.1 for measurement methods. > Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms. > > -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor. > -- The pink trace was adding a 10 nF cap across the input. > -- The green trace was unplugging my laptop switching power supply from the same outlet! > -- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way. > > My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/ > > My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab. Well, if you are happy with that, fine. But there are many things happening on the grid which needs deep analysis and the tools for it has been developed to provide both resolution and removal of noise which is not part of the measurments. Just calibrating the trigger noise for a PMU requires care, as the S/N required for a straight comparator for the applications is several tens of dBs away from a good conditions, so they have had issues with doing that. Doing your own time-stamping like you have done is naturally fun, but do not confuse it with the experience and processing that have been shown needed by an industry. BTW. WECC, who has a large network of PMUs, and that covers where you have your house and measurement point, can't release detailed data to me or you just for fun. It always needs to be cleared from a security point of view. Cheers, Magnus
TK
Tom Knox
Wed, Mar 12, 2014 5:15 PM

So we know there are deviations in line freq. But it seems strange in this era of very accurate and inexpensive freq references.
How much is related to the generation? It seems in this era of switching supplies and other complex loads that even if the power were perfect at the generator the phase/freq could vary widely across the grid as different parts of the sine wave are loaded in a non linear fashion. And could a small digital signal be added to the smart grid that would control switching supplies to correct rather then degrade the grid signal?

Thomas Knox

Date: Wed, 12 Mar 2014 16:39:50 +0100
From: magnus@rubidium.dyndns.org
To: time-nuts@febo.com
Subject: Re: [time-nuts] Mains frequency

Tom,

On 18/11/13 23:15, Tom Van Baak wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot?

I don't have much of that myself. I do recommend you to check the
presentations of the NASPI conference (naspi.org). There is plenty of
plots there.

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do.

Well, I should toss that over to the good folk at NIST doing
synchrophasor calibrations. Should I grab them now that we are in the
same room?

Have a look at IEEE C37.118.1 for measurement methods.

Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way.

My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab.

Well, if you are happy with that, fine. But there are many things
happening on the grid which needs deep analysis and the tools for it has
been developed to provide both resolution and removal of noise which is
not part of the measurments. Just calibrating the trigger noise for a
PMU requires care, as the S/N required for a straight comparator for the
applications is several tens of dBs away from a good conditions, so they
have had issues with doing that.

Doing your own time-stamping like you have done is naturally fun, but do
not confuse it with the experience and processing that have been shown
needed by an industry.

BTW. WECC, who has a large network of PMUs, and that covers where you
have your house and measurement point, can't release detailed data to me
or you just for fun. It always needs to be cleared from a security point
of view.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

So we know there are deviations in line freq. But it seems strange in this era of very accurate and inexpensive freq references. How much is related to the generation? It seems in this era of switching supplies and other complex loads that even if the power were perfect at the generator the phase/freq could vary widely across the grid as different parts of the sine wave are loaded in a non linear fashion. And could a small digital signal be added to the smart grid that would control switching supplies to correct rather then degrade the grid signal? Thomas Knox > Date: Wed, 12 Mar 2014 16:39:50 +0100 > From: magnus@rubidium.dyndns.org > To: time-nuts@febo.com > Subject: Re: [time-nuts] Mains frequency > > Tom, > > On 18/11/13 23:15, Tom Van Baak wrote: > > Magnus, > > > > I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot? > > I don't have much of that myself. I do recommend you to check the > presentations of the NASPI conference (naspi.org). There is plenty of > plots there. > > > I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do. > > Well, I should toss that over to the good folk at NIST doing > synchrophasor calibrations. Should I grab them now that we are in the > same room? > > Have a look at IEEE C37.118.1 for measurement methods. > > > Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms. > > > > -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor. > > -- The pink trace was adding a 10 nF cap across the input. > > -- The green trace was unplugging my laptop switching power supply from the same outlet! > > -- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way. > > > > My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/ > > > > My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab. > > Well, if you are happy with that, fine. But there are many things > happening on the grid which needs deep analysis and the tools for it has > been developed to provide both resolution and removal of noise which is > not part of the measurments. Just calibrating the trigger noise for a > PMU requires care, as the S/N required for a straight comparator for the > applications is several tens of dBs away from a good conditions, so they > have had issues with doing that. > > Doing your own time-stamping like you have done is naturally fun, but do > not confuse it with the experience and processing that have been shown > needed by an industry. > > BTW. WECC, who has a large network of PMUs, and that covers where you > have your house and measurement point, can't release detailed data to me > or you just for fun. It always needs to be cleared from a security point > of view. > > Cheers, > Magnus > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.