That's no true, at least in my country. The industrial
consumer is charged for reactive power. We are therefore
forced to correct our power factor (cos fi).
Antonio
CT1TE
Quoting "J. Forster" jfor@quik.com:
Power companies charge for KVAs, NOT KVARs.
-John
=================
Take a look at the poor (but commonly low) power factor.
Much more volt-amps are being delivered than used to do effective work
as kilowatts.
Power factor correction would be a money saver if saving money were an
objective.
Stan, W1LE Cape Cod
Poul-Henning Kamp wrote:
In message B8DD8AD0-9A4D-4332-83A5-0669685A2671@cq.nu, Bob Camp
writes:
Hi
I wonder what just the electric bill is to keep a single chain (4
transmitters) up and running?
http://phk.freebsd.dk/photos/L9007M/dscf0458.jpg.html
Looks like 40kW for a dualrated transmitter like EidÃ
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
A FCUP utiliza o sistema open source de webmail Horde/IMP (www.horde.org)
Visite: http://www.fc.up.pt/ http://info.fc.up.pt/
That's more in line with what I've seen... billing for KVA plus a penalty
for high KVARs.
Interestingly, last seen, the giant wound-rotor synchronous motors at the
Bitter National Lab got a rate reduction for overexciting the rotors, so
they look like capacitors, rather than inductors.
-John
=============
On 2/14/10 12:54 PM, "J. Forster" jfor@quik.com wrote:
Power companies charge for KVAs, NOT KVARs.
-John
=================
Take a look at the poor (but commonly low) power factor.
Much more volt-amps are being delivered than used to do effective work
as kilowatts.
Power factor correction would be a money saver if saving money were an
objective.
PF = 0.75 isn't horrible but not great. The apparent power is 33% more
than
the actual power. That's what lots of places with older motors and
conventional fluorescent ballasts probably run.
The electric company (at least here in southern california) doesn't charge
for KVA or KVAR, per se. What they do is charge for kWhr, plus a penalty
for poor PF, but the penalty isn't proportional to the VARs. It's more of
a
step function, based on the peak reactive load. (measured in some fairly
small time increment)
For instance, on Southern California Edison tariff RTP-3 Large Realtime
pricing
For service delivered and metered at voltages greater than 50kV,
including Cogeneration and Small Power Production Customers, the billing
will be increased by $0.18 per kilovar of maximum reactive
demand imposed on the Company. (you get a 10%+ discount for getting your
power at 50kV and above)
For service delivered and metered at voltages of 50kV or less, including
Cogeneration and Small Power Production Customers, the billing will be
increased by $0.23 per kilovar of maximum reactive demand imposed on
the Company.