Some people didn't seam to appreciate my hydraulic air compressor and
alternator concept, so I thought I'd provide a quantitative example to
illustrate the point.
Executive summary:
Since the DC system is sized to the average load and the AC generator is
sized to the peak loads, the AC generator requires over twice the
horsepower of the DC system, which offsets the added cost of the extra
inverters required for the DC system. If hydraulic are already onboard,
say for the get-home-drive, then the DC system is $3,463 or 20.3%
cheaper than an AC generator. The DC system will provide lower operation
and maintenance cost, so it will save money in the long run. In very hot
conditions the AC generator will need to run almost continuously to
provide air conditioning, whereas the DC system will run 8.5 hours per
day in 2 hour runs separated by 4 hour calms with the A/C running off
the battery bank. Although the hydraulic system seams complex, it will
be purchased as a palletized and pre-tested system and maintenance and
operation will be no more complex than a conventional generator albeit
less conventional. Hydraulic drives on the alternators allow then to
produce maximum power independent of engine speed (provided it is
producing enough power to run the alternators) and more power at low
engine speed than belt driven alternators.
The gory detail:
The smallest air compressor for the SCUBA tanks that I can find is the
Bauer Junior Compressor with a 3 HP electric motor. According to Bauer
it takes 17 amps steady state and 90 amps for startup which is a ratio
of 5.2 and in the normal range for induction motors. They also claim it
will operate on an 8 KW generator although I calculate that it should
have a 10KW generator ideally.
An example of an 8 KW generator is the 8 KW Northern Lights M753Ka which
costs $8,021 at http://www.clis.com/mmarine/NorthernLights.htm and
weighs 529 LBS.
Another option is the 8 kW Spartan Series Marine Generators with an
Isuzu Diesel Engine which costs $4,299 @
(http://www.americasgenerators.com/products/product_view.php?ProductID=8
73 ) and weighs 446 lbs. This engine is rated at 22.4 BHP Continuous @
3000 RPM (http://www.frontierequip.com/isuzu/isuzu.htm). Now if you are
wondering why it takes a 22.4 HP engine to drive an 8 KW generator i.e.
10.7 HP output, there are three reasons. First the generator runs at
1800 RPM to produce 60 Hz power and the power rating at 1800 RPM is 15.4
HP continuous (http://www.tuban.net/Model8_5Isuzu60HzDataSheet.html ).
Second most generators operate at ~10 to 20% power margin to assure they
can maintain the required speed (this is where many manufacturers cheat
to get cost down). I calculate the Spartan power margin at 10.7
/(15.4*.85) = .817 or 18.3%. Third the typical AC generator efficiency
is ~85% so output or 7.8 KW.
Using a hydraulic pump and motor with a 70% power transmission
efficiency (typical for a well designed system) would require a 4.3 HP
diesel engine minimum. One example of a liquid cooled marine diesel is
the Kubota Z482E which is rated at 10.4 HP continuous and weighs 117 lbs
with an end plate and 179 with SAE flywheel housing
(http://www.frontierequip.com/kubota/kubota.htm ). The Z482E would need
to run at 1800 RPM to produce 4.2 BHP. The Z482 cost US$2,617
(http://www.rs-refrigeration.co.uk/Kubo.asp ). Without taking the time
to engineer the hydraulics system, I anticipate the cost of the
hydraulics will be far less than the cost difference between the
Northern Lights 8KW generator and the Kubota and a little higher than
the cost differential relative to the 8 kW Spartan generator. However
operation and maintenance costs for the smaller Kubota should be
significantly lower.
Even though I am a Mechanical Engineer and I could design this system
myself, I would contract the design and assembly of the complete system
to professionals such at Frontier Equipment who provide custom auxiliary
design assembly services
(http://www.frontierequip.com/powerunit/marineaux.htm ). I would have it
built-up, tested and delivered as a palletized subassembly. Take a look
at some of the examples they provide, some of them are close to what I
am proposing.
Next I'd like to consider the total electrical requirements of the boat.
I've started a generator load estimating spread sheet and uploaded it to
my web site www.portager.info the direct link is
http://www.portager.info/generator_loads.htm . I also provided links to
down load Excel 2002 or Excel 5/95 versions of the workbook. I used a
list of loads intended for home use, so there are still some items in
the list that don't belong. These loads are only preliminary estimates
intended for comparison purposes. I sized the DC refrigerator/freezer
load at 65 watts/hr so I just entered it as a 65 watt DC load with a
100% duty cycle.
Load case #1 shows everything I think I might want to be able to run at
the same time with an electric air compressor. This is a worst case day
where both A/C systems are running with a 50% duty cycle, i.e. the
hottest day the boat should ever see. You will notice that I have
included a combo washer/dryer, dishwasher, convection oven, ... I figure
if I'm going to have my air compressor how can a deny the Admirable her
quality of life? In the startup load calculations, I assumed that the
startup loads are short in duration and therefore they never occur
simultaneously (not necessarily a good assumption). In this case the
steady state power load is 12.3 KW and the peak load is 20.4 KW so I
rounded down to 20 KW. Load 2 is the same except the air compressor is
hydraulic. In this case the steady state load is 10.4 KW and the peak
load is 13.2 KW. So using the hydraulically powered air compressor
allows the generator to be reduced from 20 KW to 12 KW (I rounded down
to 12 KW since the next step up was 16 KW). Using Northern Lights
generators the cost savings is $4,616 and the weight savings is 262 lbs.
Load case #3 uses the 18,000 BTU Flagship Marine heat pumps instead of
the HFL 16,000 BTU air conditioners. I used the cooling steady state
power requirement instead of the greater of the two (heating), because
the duty cycle is worse in the cooling mode. Despite the slightly higher
steady state power requirement, due to the lower startup load, the
required generator size decreases 1 KW, however this benefit just adds
reduces the negative margin. The primary feature of the Flagship Marine
heat pump is that it does double duty by providing both heating and
cooling.
Column "K" provides an estimated duty cycle and column "L" provides the
average power per day, which is used to determine the DC generator run
time. Cell L158 provides the DC power input to the invertors to run the
AC loads and cell O159 provides the total DC load. Note that in load
case #1, the AC generator required a 20 KW capacity while the DC load is
only 2.5 KW after accounting for the inverter efficiency. Adding in the
DC load brings the total to 3.2 KW. I know this seams like I'm an
incredible power hog, but it is the hottest day of the year and it is
only an example. Load case #2 requires 13.2 KW AC versus 2.4 KW DC and
load case #3 requires 12.3 KW AC versus 2.8 KW DC.
In calculating the alternator output, I deducted 10% for hot operating
conditions. To determine the alternator output of the belt driven
alternators I set the drive ratio so that the alternator speed is = the
rated speed when the engine is running at 3,600 rpm. I then determined
the output with the engine operating at 1,800 rpm. For the hydraulic
alternator I assumed the alternator would operate at 5,000 rpm. Note
that since the 98-24-220-BL has a maximum speed of 6,000 rpm, the
hydraulic alternator has a 22% higher output when the engine is running
at 1800 rpm than the same alternator with belt drive. If the engine
speed drops to 1200 rpm the hydraulic alternator produces 52% more power
than the belt drive alternator. At 900 rpm the difference is 78%
(assuming the engine produces enough power at 900 rpm to drive the
alternator). Since the 97-24-140-BL alternator has a maximum speed of
10,000 lbs the maximum drive ratio is 2.78:1, so with the engine
operating at 1800 rpm it produces its full rated 140 amps but 39% loss
than the hydraulic 98-24-220-BL. At 1200 rpm the 97-24-140-BL produces
44% less power and at 900 rpm 50% less. The real benefit of the
hydraulic alternator is if the engine is oversized for the alternator.
In other words if the auxiliary is sized at 40 HP for the get home drive
and the maximum alternator load is 12.3 HP, when only the alternators
are on the engine will be able to slow down and still provide maximum
power output. With one 98-24-220-BL alternators the output is 5.5 KW of
24 VDC and the run time is 17 hours o the hottest day of the year. With
two 98-24-220-BL alternators the output is 11 KW and the engine run time
is 8.5 hours and the time to recharge the battery bank is <1 hour.
Finally, I estimated the weight and cost of the all AC and all DC
alternatives. The DC system turned out $1,062 or 6.2% higher cost which
is ~8.1% higher than the AC system, however the DC system will have
significantly lower operating cost and shorter run time. In addition,
the DC system is 358 lbs or 34% lighter than the AC system. Finally,
cell E47 shows that if hydraulic system is already onboard, say for a
get-home-drive, then the DC system is $3,463 or 20.3% cheaper than an AC
generator.
Regards;
Mike Schooley
Designing "Portager" a transportable trawler