Mains frequency

BD
Bill Dailey
Sat, Nov 16, 2013 2:51 AM

I have my picpet faithfully measuring grid frequency and was wondering if anyone else if the eastern grid has a live measure to compare to?

110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log freq every second.

Sent from mobile

I have my picpet faithfully measuring grid frequency and was wondering if anyone else if the eastern grid has a live measure to compare to? 110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log freq every second. Sent from mobile
KM
Kevin M. Rosenberg
Sat, Nov 16, 2013 7:55 AM

Not on the eastern grid, but I had hook my picpet ac mains logger back to the southwest grid if that would be of any help.

On Nov 15, 2013, at 7:51 PM, Bill Dailey docdailey@gmail.com wrote:

I have my picpet faithfully measuring grid frequency and was wondering if anyone else if the eastern grid has a live measure to compare to?

110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log freq every second.

Sent from mobile


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Not on the eastern grid, but I had hook my picpet ac mains logger back to the southwest grid if that would be of any help. On Nov 15, 2013, at 7:51 PM, Bill Dailey <docdailey@gmail.com> wrote: > I have my picpet faithfully measuring grid frequency and was wondering if anyone else if the eastern grid has a live measure to compare to? > > 110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log freq every second. > > Sent from mobile > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BD
Bill Dailey
Sat, Nov 16, 2013 8:02 AM

would probably be an interesting comparison.  I am working with a guy on
the eastern grid part now.

You arent using python for processing on the pc are you?  If so, I would be
interested in your script.  I am trying to verify I am not a just a little
off with mine.

Bill

On Sat, Nov 16, 2013 at 1:55 AM, Kevin M. Rosenberg kevin@rosenberg.netwrote:

Not on the eastern grid, but I had hook my picpet ac mains logger back to
the southwest grid if that would be of any help.

On Nov 15, 2013, at 7:51 PM, Bill Dailey docdailey@gmail.com wrote:

I have my picpet faithfully measuring grid frequency and was wondering

if anyone else if the eastern grid has a live measure to compare to?

110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles-->

log freq every second.

Sent from mobile


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO

would probably be an interesting comparison. I am working with a guy on the eastern grid part now. You arent using python for processing on the pc are you? If so, I would be interested in your script. I am trying to verify I am not a just a little off with mine. Bill On Sat, Nov 16, 2013 at 1:55 AM, Kevin M. Rosenberg <kevin@rosenberg.net>wrote: > Not on the eastern grid, but I had hook my picpet ac mains logger back to > the southwest grid if that would be of any help. > > On Nov 15, 2013, at 7:51 PM, Bill Dailey <docdailey@gmail.com> wrote: > > > I have my picpet faithfully measuring grid frequency and was wondering > if anyone else if the eastern grid has a live measure to compare to? > > > > 110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> > log freq every second. > > > > Sent from mobile > > _______________________________________________ > > time-nuts mailing list -- time-nuts@febo.com > > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > > and follow the instructions there. > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Doc Bill Dailey KXØO
CA
Chris Albertson
Sat, Nov 16, 2013 8:29 AM

Here is a real-time map of mains frequency
http://fnetpublic.utk.edu/gradientmap.html

A common way to measure this is to connect a 9 volt AC plug-in power supply
to the DCD pin of a serial port and let the PPS system log and time stamp
each cycle.  You can do it no more hardware than the transformer and any
PC-like computer.  The computer can bedding other tasks at the same time,
like serving files or whatever.

On Fri, Nov 15, 2013 at 6:51 PM, Bill Dailey docdailey@gmail.com wrote:

I have my picpet faithfully measuring grid frequency and was wondering if
anyone else if the eastern grid has a live measure to compare to?

110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log
freq every second.

Sent from mobile


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California

Here is a real-time map of mains frequency http://fnetpublic.utk.edu/gradientmap.html A common way to measure this is to connect a 9 volt AC plug-in power supply to the DCD pin of a serial port and let the PPS system log and time stamp each cycle. You can do it no more hardware than the transformer and any PC-like computer. The computer can bedding other tasks at the same time, like serving files or whatever. On Fri, Nov 15, 2013 at 6:51 PM, Bill Dailey <docdailey@gmail.com> wrote: > I have my picpet faithfully measuring grid frequency and was wondering if > anyone else if the eastern grid has a live measure to compare to? > > 110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log > freq every second. > > Sent from mobile > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Chris Albertson Redondo Beach, California
CA
Chris Albertson
Sat, Nov 16, 2013 8:52 AM

Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

On Fri, Nov 15, 2013 at 6:51 PM, Bill Dailey docdailey@gmail.com wrote:

110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log
freq every second.

--

Chris Albertson
Redondo Beach, California

Your method tosses out a lot of data. You can't see transients. Ideally rather then record a 1 second average you'd record the time of EVERY zero crossing. It sounds like a lot of data but not really. You only record 32 bits 60 times each second. That is 240 bytes per second. On Fri, Nov 15, 2013 at 6:51 PM, Bill Dailey <docdailey@gmail.com> wrote: > > 110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log > freq every second. -- Chris Albertson Redondo Beach, California
MD
Magnus Danielson
Sat, Nov 16, 2013 8:52 AM

On 11/16/2013 08:55 AM, Kevin M. Rosenberg wrote:

Not on the eastern grid, but I had hook my picpet ac mains logger back to the southwest grid if that would be of any help.

They are separated, so they are not phase coherent. Texas is it's own
grid too.

Cheers,
Magnus

On Nov 15, 2013, at 7:51 PM, Bill Dailey docdailey@gmail.com wrote:

I have my picpet faithfully measuring grid frequency and was wondering if anyone else if the eastern grid has a live measure to compare to?

110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log freq every second.

Sent from mobile


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

On 11/16/2013 08:55 AM, Kevin M. Rosenberg wrote: > Not on the eastern grid, but I had hook my picpet ac mains logger back to the southwest grid if that would be of any help. They are separated, so they are not phase coherent. Texas is it's own grid too. Cheers, Magnus > > On Nov 15, 2013, at 7:51 PM, Bill Dailey <docdailey@gmail.com> wrote: > >> I have my picpet faithfully measuring grid frequency and was wondering if anyone else if the eastern grid has a live measure to compare to? >> >> 110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log freq every second. >> >> Sent from mobile >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BD
Bill Dailey
Sat, Nov 16, 2013 9:02 AM

Understood.. I have it every 6 cycles now to sync up with his
synchrophaser.  I wrote the script so I can specify the number of cycles I
average.  Right now it is at 6 because his measures are every 0.1s.

On Sat, Nov 16, 2013 at 2:52 AM, Chris Albertson
albertson.chris@gmail.comwrote:

Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

On Fri, Nov 15, 2013 at 6:51 PM, Bill Dailey docdailey@gmail.com wrote:

110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log
freq every second.

--

Chris Albertson
Redondo Beach, California


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO

Understood.. I have it every 6 cycles now to sync up with his synchrophaser. I wrote the script so I can specify the number of cycles I average. Right now it is at 6 because his measures are every 0.1s. On Sat, Nov 16, 2013 at 2:52 AM, Chris Albertson <albertson.chris@gmail.com>wrote: > Your method tosses out a lot of data. You can't see transients. Ideally > rather then record a 1 second average you'd record the time of EVERY zero > crossing. It sounds like a lot of data but not really. You only record > 32 bits 60 times each second. That is 240 bytes per second. > > On Fri, Nov 15, 2013 at 6:51 PM, Bill Dailey <docdailey@gmail.com> wrote: > > > > > 110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> log > > freq every second. > > > -- > > Chris Albertson > Redondo Beach, California > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Doc Bill Dailey KXØO
BD
Bill Dailey
Sat, Nov 16, 2013 9:05 AM

rough comparison... I didnt have my interval right for this set.

https://www.dropbox.com/s/1gi5tbf96yop5hz/stonercompare.JPG

On Sat, Nov 16, 2013 at 3:02 AM, Bill Dailey docdailey@gmail.com wrote:

Understood.. I have it every 6 cycles now to sync up with his
synchrophaser.  I wrote the script so I can specify the number of cycles I
average.  Right now it is at 6 because his measures are every 0.1s.

On Sat, Nov 16, 2013 at 2:52 AM, Chris Albertson <
albertson.chris@gmail.com> wrote:

Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

On Fri, Nov 15, 2013 at 6:51 PM, Bill Dailey docdailey@gmail.com wrote:

110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles-->

log

freq every second.

--

Chris Albertson
Redondo Beach, California


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO

--
Doc

Bill Dailey
KXØO

rough comparison... I didnt have my interval right for this set. https://www.dropbox.com/s/1gi5tbf96yop5hz/stonercompare.JPG On Sat, Nov 16, 2013 at 3:02 AM, Bill Dailey <docdailey@gmail.com> wrote: > Understood.. I have it every 6 cycles now to sync up with his > synchrophaser. I wrote the script so I can specify the number of cycles I > average. Right now it is at 6 because his measures are every 0.1s. > > > On Sat, Nov 16, 2013 at 2:52 AM, Chris Albertson < > albertson.chris@gmail.com> wrote: > >> Your method tosses out a lot of data. You can't see transients. Ideally >> rather then record a 1 second average you'd record the time of EVERY zero >> crossing. It sounds like a lot of data but not really. You only record >> 32 bits 60 times each second. That is 240 bytes per second. >> >> On Fri, Nov 15, 2013 at 6:51 PM, Bill Dailey <docdailey@gmail.com> wrote: >> >> > >> > 110vac-->5vac-->100ohm-->picpet event---> python average 60 cycles--> >> log >> > freq every second. >> >> >> -- >> >> Chris Albertson >> Redondo Beach, California >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > > > > -- > Doc > > Bill Dailey > KXØO > > > > > -- Doc Bill Dailey KXØO
MD
Magnus Danielson
Sat, Nov 16, 2013 9:18 AM

On 11/16/2013 09:52 AM, Chris Albertson wrote:

Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus

On 11/16/2013 09:52 AM, Chris Albertson wrote: > Your method tosses out a lot of data. You can't see transients. Ideally > rather then record a 1 second average you'd record the time of EVERY zero > crossing. It sounds like a lot of data but not really. You only record > 32 bits 60 times each second. That is 240 bytes per second. But you want it filtered to avoid the transients. Those are really not that interesting when you measure the grid. Also, if you use the event trigger method you probably want to use an amplifier to increase the slew-rate such that noise does not convert into time jitter. Cheers, Magnus
CH
Chuck Harris
Sat, Nov 16, 2013 2:13 PM

Random noise always converts into time jitter.  It doesn't
matter how much you amplify the input signal, noise can push
the detected zero crossing wherever it wants to.

-Chuck Harris

Magnus Danielson wrote:

On 11/16/2013 09:52 AM, Chris Albertson wrote:

Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Random noise always converts into time jitter. It doesn't matter how much you amplify the input signal, noise can push the detected zero crossing wherever it wants to. -Chuck Harris Magnus Danielson wrote: > On 11/16/2013 09:52 AM, Chris Albertson wrote: >> Your method tosses out a lot of data. You can't see transients. Ideally >> rather then record a 1 second average you'd record the time of EVERY zero >> crossing. It sounds like a lot of data but not really. You only record >> 32 bits 60 times each second. That is 240 bytes per second. > But you want it filtered to avoid the transients. Those are really not > that interesting when you measure the grid. > > Also, if you use the event trigger method you probably want to use an > amplifier to increase the slew-rate such that noise does not convert > into time jitter. > > Cheers, > Magnus > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. >
CA
Chris Albertson
Sat, Nov 16, 2013 5:26 PM

The signal is 120 volts.  You hardly need to amplify it.  Clip it with a
diode to +- 9 volts so as not to blow up your serial port.  But I'd use a
transformer for safety. The zero crossing detectors are built into the
RS232 interface.    You take advantage of the RS232 spec which has a DCD
pin input of about +-9 volts that is already set up to find a leading edge
of a pulse and cause a very low latency interrupt.  The system software
already will capture the time all inside a kernel level interrupt handler.

The jitter turns out to be on the order of a single digit microseconds.
Good enough for measuring a 60Hz signal.

I guess if you want to see transients depends on the purpose of the
experiment.  Are you looking at local AC power quality or wanting to
measure the grid.  The grid is well monitored, just use FNET and you get
real-time data for all of North America.  I think the reason for measuring
it yourself is to see local power quality and things load switching inside
your own building, that's transients.

The other way to measure AC with zero added equipment is to treat it as an
audio signal and after reducing it to 1 volt run it into an audio interface
And then use FFT.  This will let you see very small spikes and noise.  It
depends again on your purpose for doing this.

On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson <
magnus@rubidium.dyndns.org> wrote:

On 11/16/2013 09:52 AM, Chris Albertson wrote:

Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California

The signal is 120 volts. You hardly need to amplify it. Clip it with a diode to +- 9 volts so as not to blow up your serial port. But I'd use a transformer for safety. The zero crossing detectors are built into the RS232 interface. You take advantage of the RS232 spec which has a DCD pin input of about +-9 volts that is already set up to find a leading edge of a pulse and cause a very low latency interrupt. The system software already will capture the time all inside a kernel level interrupt handler. The jitter turns out to be on the order of a single digit microseconds. Good enough for measuring a 60Hz signal. I guess if you want to see transients depends on the purpose of the experiment. Are you looking at local AC power quality or wanting to measure the grid. The grid is well monitored, just use FNET and you get real-time data for all of North America. I think the reason for measuring it yourself is to see local power quality and things load switching inside your own building, that's transients. The other way to measure AC with zero added equipment is to treat it as an audio signal and after reducing it to 1 volt run it into an audio interface And then use FFT. This will let you see very small spikes and noise. It depends again on your purpose for doing this. On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson < magnus@rubidium.dyndns.org> wrote: > On 11/16/2013 09:52 AM, Chris Albertson wrote: > > Your method tosses out a lot of data. You can't see transients. Ideally > > rather then record a 1 second average you'd record the time of EVERY zero > > crossing. It sounds like a lot of data but not really. You only record > > 32 bits 60 times each second. That is 240 bytes per second. > But you want it filtered to avoid the transients. Those are really not > that interesting when you measure the grid. > > Also, if you use the event trigger method you probably want to use an > amplifier to increase the slew-rate such that noise does not convert > into time jitter. > > Cheers, > Magnus > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Chris Albertson Redondo Beach, California
BD
Bill Dailey
Sat, Nov 16, 2013 7:23 PM

My purpose is to do it with a picpet.  That's it.  So, that eliminates a bunch of the options.  I can decouple the measurements from the pc clock that way.

Doc

Sent from mobile

On Nov 16, 2013, at 11:26 AM, Chris Albertson albertson.chris@gmail.com wrote:

The signal is 120 volts.  You hardly need to amplify it.  Clip it with a
diode to +- 9 volts so as not to blow up your serial port.  But I'd use a
transformer for safety. The zero crossing detectors are built into the
RS232 interface.    You take advantage of the RS232 spec which has a DCD
pin input of about +-9 volts that is already set up to find a leading edge
of a pulse and cause a very low latency interrupt.  The system software
already will capture the time all inside a kernel level interrupt handler.

The jitter turns out to be on the order of a single digit microseconds.
Good enough for measuring a 60Hz signal.

I guess if you want to see transients depends on the purpose of the
experiment.  Are you looking at local AC power quality or wanting to
measure the grid.  The grid is well monitored, just use FNET and you get
real-time data for all of North America.  I think the reason for measuring
it yourself is to see local power quality and things load switching inside
your own building, that's transients.

The other way to measure AC with zero added equipment is to treat it as an
audio signal and after reducing it to 1 volt run it into an audio interface
And then use FFT.  This will let you see very small spikes and noise.  It
depends again on your purpose for doing this.

On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson <
magnus@rubidium.dyndns.org> wrote:

On 11/16/2013 09:52 AM, Chris Albertson wrote:
Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

My purpose is to do it with a picpet. That's it. So, that eliminates a bunch of the options. I can decouple the measurements from the pc clock that way. Doc Sent from mobile > On Nov 16, 2013, at 11:26 AM, Chris Albertson <albertson.chris@gmail.com> wrote: > > The signal is 120 volts. You hardly need to amplify it. Clip it with a > diode to +- 9 volts so as not to blow up your serial port. But I'd use a > transformer for safety. The zero crossing detectors are built into the > RS232 interface. You take advantage of the RS232 spec which has a DCD > pin input of about +-9 volts that is already set up to find a leading edge > of a pulse and cause a very low latency interrupt. The system software > already will capture the time all inside a kernel level interrupt handler. > > The jitter turns out to be on the order of a single digit microseconds. > Good enough for measuring a 60Hz signal. > > I guess if you want to see transients depends on the purpose of the > experiment. Are you looking at local AC power quality or wanting to > measure the grid. The grid is well monitored, just use FNET and you get > real-time data for all of North America. I think the reason for measuring > it yourself is to see local power quality and things load switching inside > your own building, that's transients. > > > > The other way to measure AC with zero added equipment is to treat it as an > audio signal and after reducing it to 1 volt run it into an audio interface > And then use FFT. This will let you see very small spikes and noise. It > depends again on your purpose for doing this. > > > > > On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson < > magnus@rubidium.dyndns.org> wrote: > >>> On 11/16/2013 09:52 AM, Chris Albertson wrote: >>> Your method tosses out a lot of data. You can't see transients. Ideally >>> rather then record a 1 second average you'd record the time of EVERY zero >>> crossing. It sounds like a lot of data but not really. You only record >>> 32 bits 60 times each second. That is 240 bytes per second. >> But you want it filtered to avoid the transients. Those are really not >> that interesting when you measure the grid. >> >> Also, if you use the event trigger method you probably want to use an >> amplifier to increase the slew-rate such that noise does not convert >> into time jitter. >> >> Cheers, >> Magnus >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > > > > -- > > Chris Albertson > Redondo Beach, California > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
MD
Magnus Danielson
Sat, Nov 16, 2013 7:47 PM

On 11/16/2013 03:13 PM, Chuck Harris wrote:

Random noise always converts into time jitter.  It doesn't
matter how much you amplify the input signal, noise can push
the detected zero crossing wherever it wants to.

You are missing that you can alter how much trigger jitter you get.

Cheers,
Magnus

-Chuck Harris

Magnus Danielson wrote:

On 11/16/2013 09:52 AM, Chris Albertson wrote:

Your method tosses out a lot of data.  You can't see transients.
Ideally
rather then record a 1 second average you'd record the time of EVERY
zero
crossing.  It sounds like a lot of data but not really.  You only
record
32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

On 11/16/2013 03:13 PM, Chuck Harris wrote: > Random noise always converts into time jitter. It doesn't > matter how much you amplify the input signal, noise can push > the detected zero crossing wherever it wants to. You are missing that you can alter how much trigger jitter you get. Cheers, Magnus > > -Chuck Harris > > Magnus Danielson wrote: >> On 11/16/2013 09:52 AM, Chris Albertson wrote: >>> Your method tosses out a lot of data. You can't see transients. >>> Ideally >>> rather then record a 1 second average you'd record the time of EVERY >>> zero >>> crossing. It sounds like a lot of data but not really. You only >>> record >>> 32 bits 60 times each second. That is 240 bytes per second. >> But you want it filtered to avoid the transients. Those are really not >> that interesting when you measure the grid. >> >> Also, if you use the event trigger method you probably want to use an >> amplifier to increase the slew-rate such that noise does not convert >> into time jitter. >> >> Cheers, >> Magnus >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
TV
Tom Van Baak (lab)
Sat, Nov 16, 2013 7:53 PM

Doc,

I measure mains time & frequency with a picPET all the time. In fact that's one of the reasons I designed it. If you're having any trouble contact me by email.

/tvb (i5s)

On Nov 16, 2013, at 11:23 AM, Bill Dailey docdailey@gmail.com wrote:

My purpose is to do it with a picpet.  That's it.  So, that eliminates a bunch of the options.  I can decouple the measurements from the pc clock that way.

Doc

Sent from mobile

On Nov 16, 2013, at 11:26 AM, Chris Albertson albertson.chris@gmail.com wrote:

The signal is 120 volts.  You hardly need to amplify it.  Clip it with a
diode to +- 9 volts so as not to blow up your serial port.  But I'd use a
transformer for safety. The zero crossing detectors are built into the
RS232 interface.    You take advantage of the RS232 spec which has a DCD
pin input of about +-9 volts that is already set up to find a leading edge
of a pulse and cause a very low latency interrupt.  The system software
already will capture the time all inside a kernel level interrupt handler.

The jitter turns out to be on the order of a single digit microseconds.
Good enough for measuring a 60Hz signal.

I guess if you want to see transients depends on the purpose of the
experiment.  Are you looking at local AC power quality or wanting to
measure the grid.  The grid is well monitored, just use FNET and you get
real-time data for all of North America.  I think the reason for measuring
it yourself is to see local power quality and things load switching inside
your own building, that's transients.

The other way to measure AC with zero added equipment is to treat it as an
audio signal and after reducing it to 1 volt run it into an audio interface
And then use FFT.  This will let you see very small spikes and noise.  It
depends again on your purpose for doing this.

On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson <
magnus@rubidium.dyndns.org> wrote:

On 11/16/2013 09:52 AM, Chris Albertson wrote:
Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Doc, I measure mains time & frequency with a picPET all the time. In fact that's one of the reasons I designed it. If you're having any trouble contact me by email. /tvb (i5s) > On Nov 16, 2013, at 11:23 AM, Bill Dailey <docdailey@gmail.com> wrote: > > My purpose is to do it with a picpet. That's it. So, that eliminates a bunch of the options. I can decouple the measurements from the pc clock that way. > > Doc > > Sent from mobile > >> On Nov 16, 2013, at 11:26 AM, Chris Albertson <albertson.chris@gmail.com> wrote: >> >> The signal is 120 volts. You hardly need to amplify it. Clip it with a >> diode to +- 9 volts so as not to blow up your serial port. But I'd use a >> transformer for safety. The zero crossing detectors are built into the >> RS232 interface. You take advantage of the RS232 spec which has a DCD >> pin input of about +-9 volts that is already set up to find a leading edge >> of a pulse and cause a very low latency interrupt. The system software >> already will capture the time all inside a kernel level interrupt handler. >> >> The jitter turns out to be on the order of a single digit microseconds. >> Good enough for measuring a 60Hz signal. >> >> I guess if you want to see transients depends on the purpose of the >> experiment. Are you looking at local AC power quality or wanting to >> measure the grid. The grid is well monitored, just use FNET and you get >> real-time data for all of North America. I think the reason for measuring >> it yourself is to see local power quality and things load switching inside >> your own building, that's transients. >> >> >> >> The other way to measure AC with zero added equipment is to treat it as an >> audio signal and after reducing it to 1 volt run it into an audio interface >> And then use FFT. This will let you see very small spikes and noise. It >> depends again on your purpose for doing this. >> >> >> >> >> On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson < >> magnus@rubidium.dyndns.org> wrote: >> >>>> On 11/16/2013 09:52 AM, Chris Albertson wrote: >>>> Your method tosses out a lot of data. You can't see transients. Ideally >>>> rather then record a 1 second average you'd record the time of EVERY zero >>>> crossing. It sounds like a lot of data but not really. You only record >>>> 32 bits 60 times each second. That is 240 bytes per second. >>> But you want it filtered to avoid the transients. Those are really not >>> that interesting when you measure the grid. >>> >>> Also, if you use the event trigger method you probably want to use an >>> amplifier to increase the slew-rate such that noise does not convert >>> into time jitter. >>> >>> Cheers, >>> Magnus >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to >>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >> >> >> >> -- >> >> Chris Albertson >> Redondo Beach, California >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BD
Bill Dailey
Sat, Nov 16, 2013 8:03 PM

No trouble.  Easy.  I love it.  Keeping track of the rolling counters was a hack because I am so far removed from serious programming.

Sent from mobile

On Nov 16, 2013, at 1:53 PM, "Tom Van Baak (lab)" tvb@leapsecond.com wrote:

Doc,

I measure mains time & frequency with a picPET all the time. In fact that's one of the reasons I designed it. If you're having any trouble contact me by email.

/tvb (i5s)

On Nov 16, 2013, at 11:23 AM, Bill Dailey docdailey@gmail.com wrote:

My purpose is to do it with a picpet.  That's it.  So, that eliminates a bunch of the options.  I can decouple the measurements from the pc clock that way.

Doc

Sent from mobile

On Nov 16, 2013, at 11:26 AM, Chris Albertson albertson.chris@gmail.com wrote:

The signal is 120 volts.  You hardly need to amplify it.  Clip it with a
diode to +- 9 volts so as not to blow up your serial port.  But I'd use a
transformer for safety. The zero crossing detectors are built into the
RS232 interface.    You take advantage of the RS232 spec which has a DCD
pin input of about +-9 volts that is already set up to find a leading edge
of a pulse and cause a very low latency interrupt.  The system software
already will capture the time all inside a kernel level interrupt handler.

The jitter turns out to be on the order of a single digit microseconds.
Good enough for measuring a 60Hz signal.

I guess if you want to see transients depends on the purpose of the
experiment.  Are you looking at local AC power quality or wanting to
measure the grid.  The grid is well monitored, just use FNET and you get
real-time data for all of North America.  I think the reason for measuring
it yourself is to see local power quality and things load switching inside
your own building, that's transients.

The other way to measure AC with zero added equipment is to treat it as an
audio signal and after reducing it to 1 volt run it into an audio interface
And then use FFT.  This will let you see very small spikes and noise.  It
depends again on your purpose for doing this.

On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson <
magnus@rubidium.dyndns.org> wrote:

On 11/16/2013 09:52 AM, Chris Albertson wrote:
Your method tosses out a lot of data.  You can't see transients.  Ideally
rather then record a 1 second average you'd record the time of EVERY zero
crossing.  It sounds like a lot of data but not really.  You only record
32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

No trouble. Easy. I love it. Keeping track of the rolling counters was a hack because I am so far removed from serious programming. Sent from mobile > On Nov 16, 2013, at 1:53 PM, "Tom Van Baak (lab)" <tvb@leapsecond.com> wrote: > > Doc, > > I measure mains time & frequency with a picPET all the time. In fact that's one of the reasons I designed it. If you're having any trouble contact me by email. > > /tvb (i5s) > >> On Nov 16, 2013, at 11:23 AM, Bill Dailey <docdailey@gmail.com> wrote: >> >> My purpose is to do it with a picpet. That's it. So, that eliminates a bunch of the options. I can decouple the measurements from the pc clock that way. >> >> Doc >> >> Sent from mobile >> >>> On Nov 16, 2013, at 11:26 AM, Chris Albertson <albertson.chris@gmail.com> wrote: >>> >>> The signal is 120 volts. You hardly need to amplify it. Clip it with a >>> diode to +- 9 volts so as not to blow up your serial port. But I'd use a >>> transformer for safety. The zero crossing detectors are built into the >>> RS232 interface. You take advantage of the RS232 spec which has a DCD >>> pin input of about +-9 volts that is already set up to find a leading edge >>> of a pulse and cause a very low latency interrupt. The system software >>> already will capture the time all inside a kernel level interrupt handler. >>> >>> The jitter turns out to be on the order of a single digit microseconds. >>> Good enough for measuring a 60Hz signal. >>> >>> I guess if you want to see transients depends on the purpose of the >>> experiment. Are you looking at local AC power quality or wanting to >>> measure the grid. The grid is well monitored, just use FNET and you get >>> real-time data for all of North America. I think the reason for measuring >>> it yourself is to see local power quality and things load switching inside >>> your own building, that's transients. >>> >>> >>> >>> The other way to measure AC with zero added equipment is to treat it as an >>> audio signal and after reducing it to 1 volt run it into an audio interface >>> And then use FFT. This will let you see very small spikes and noise. It >>> depends again on your purpose for doing this. >>> >>> >>> >>> >>> On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson < >>> magnus@rubidium.dyndns.org> wrote: >>> >>>>> On 11/16/2013 09:52 AM, Chris Albertson wrote: >>>>> Your method tosses out a lot of data. You can't see transients. Ideally >>>>> rather then record a 1 second average you'd record the time of EVERY zero >>>>> crossing. It sounds like a lot of data but not really. You only record >>>>> 32 bits 60 times each second. That is 240 bytes per second. >>>> But you want it filtered to avoid the transients. Those are really not >>>> that interesting when you measure the grid. >>>> >>>> Also, if you use the event trigger method you probably want to use an >>>> amplifier to increase the slew-rate such that noise does not convert >>>> into time jitter. >>>> >>>> Cheers, >>>> Magnus >>>> _______________________________________________ >>>> time-nuts mailing list -- time-nuts@febo.com >>>> To unsubscribe, go to >>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>> and follow the instructions there. >>> >>> >>> >>> -- >>> >>> Chris Albertson >>> Redondo Beach, California >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
CA
Chris Albertson
Sat, Nov 16, 2013 9:47 PM

No, I meant the purpose of the whole thing.  Why are you measuring power
frequency?  Not why are you using a PIC.    How will the data be used, what
is the question driving the measurement?

On Sat, Nov 16, 2013 at 11:23 AM, Bill Dailey docdailey@gmail.com wrote:

My purpose is to do it with a picpet.  That's it.  So, that eliminates a
bunch of the options.  I can decouple the measurements from the pc clock
that way.

Doc

Sent from mobile

On Nov 16, 2013, at 11:26 AM, Chris Albertson albertson.chris@gmail.com

wrote:

The signal is 120 volts.  You hardly need to amplify it.  Clip it with a
diode to +- 9 volts so as not to blow up your serial port.  But I'd use a
transformer for safety. The zero crossing detectors are built into the
RS232 interface.    You take advantage of the RS232 spec which has a DCD
pin input of about +-9 volts that is already set up to find a leading

edge

of a pulse and cause a very low latency interrupt.  The system software
already will capture the time all inside a kernel level interrupt

handler.

The jitter turns out to be on the order of a single digit microseconds.
Good enough for measuring a 60Hz signal.

I guess if you want to see transients depends on the purpose of the
experiment.  Are you looking at local AC power quality or wanting to
measure the grid.  The grid is well monitored, just use FNET and you get
real-time data for all of North America.  I think the reason for

measuring

it yourself is to see local power quality and things load switching

inside

your own building, that's transients.

The other way to measure AC with zero added equipment is to treat it as

an

audio signal and after reducing it to 1 volt run it into an audio

interface

And then use FFT.  This will let you see very small spikes and noise.

It

depends again on your purpose for doing this.

On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson <
magnus@rubidium.dyndns.org> wrote:

On 11/16/2013 09:52 AM, Chris Albertson wrote:
Your method tosses out a lot of data.  You can't see transients.

Ideally

rather then record a 1 second average you'd record the time of EVERY

zero

crossing.  It sounds like a lot of data but not really.  You only

record

32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California

No, I meant the purpose of the whole thing. Why are you measuring power frequency? Not why are you using a PIC. How will the data be used, what is the question driving the measurement? On Sat, Nov 16, 2013 at 11:23 AM, Bill Dailey <docdailey@gmail.com> wrote: > My purpose is to do it with a picpet. That's it. So, that eliminates a > bunch of the options. I can decouple the measurements from the pc clock > that way. > > Doc > > Sent from mobile > > > On Nov 16, 2013, at 11:26 AM, Chris Albertson <albertson.chris@gmail.com> > wrote: > > > > The signal is 120 volts. You hardly need to amplify it. Clip it with a > > diode to +- 9 volts so as not to blow up your serial port. But I'd use a > > transformer for safety. The zero crossing detectors are built into the > > RS232 interface. You take advantage of the RS232 spec which has a DCD > > pin input of about +-9 volts that is already set up to find a leading > edge > > of a pulse and cause a very low latency interrupt. The system software > > already will capture the time all inside a kernel level interrupt > handler. > > > > The jitter turns out to be on the order of a single digit microseconds. > > Good enough for measuring a 60Hz signal. > > > > I guess if you want to see transients depends on the purpose of the > > experiment. Are you looking at local AC power quality or wanting to > > measure the grid. The grid is well monitored, just use FNET and you get > > real-time data for all of North America. I think the reason for > measuring > > it yourself is to see local power quality and things load switching > inside > > your own building, that's transients. > > > > > > > > The other way to measure AC with zero added equipment is to treat it as > an > > audio signal and after reducing it to 1 volt run it into an audio > interface > > And then use FFT. This will let you see very small spikes and noise. > It > > depends again on your purpose for doing this. > > > > > > > > > > On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson < > > magnus@rubidium.dyndns.org> wrote: > > > >>> On 11/16/2013 09:52 AM, Chris Albertson wrote: > >>> Your method tosses out a lot of data. You can't see transients. > Ideally > >>> rather then record a 1 second average you'd record the time of EVERY > zero > >>> crossing. It sounds like a lot of data but not really. You only > record > >>> 32 bits 60 times each second. That is 240 bytes per second. > >> But you want it filtered to avoid the transients. Those are really not > >> that interesting when you measure the grid. > >> > >> Also, if you use the event trigger method you probably want to use an > >> amplifier to increase the slew-rate such that noise does not convert > >> into time jitter. > >> > >> Cheers, > >> Magnus > >> _______________________________________________ > >> time-nuts mailing list -- time-nuts@febo.com > >> To unsubscribe, go to > >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > >> and follow the instructions there. > > > > > > > > -- > > > > Chris Albertson > > Redondo Beach, California > > _______________________________________________ > > time-nuts mailing list -- time-nuts@febo.com > > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > > and follow the instructions there. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Chris Albertson Redondo Beach, California
DM
David Malone
Sat, Nov 16, 2013 10:06 PM

On Sat, Nov 16, 2013 at 09:26:10AM -0800, Chris Albertson wrote:

The signal is 120 volts.  You hardly need to amplify it.

I tried this a slightly different way. Since there is mains noise
everywhere, I made a small loop and connected it to a 3.5mm jack
and then plugged that into the mic socket on a sound card. You can
get lots of (slightly noisy) samples per second. I took chunks of
this data and took the Fourier transform to find the dominant
frequency:

http://www.maths.tcd.ie/~dwmalone/time/leap2012/#mains

but I guess you could filter it and count crossings too?

David.
On Sat, Nov 16, 2013 at 09:26:10AM -0800, Chris Albertson wrote: > The signal is 120 volts. You hardly need to amplify it. I tried this a slightly different way. Since there is mains noise everywhere, I made a small loop and connected it to a 3.5mm jack and then plugged that into the mic socket on a sound card. You can get lots of (slightly noisy) samples per second. I took chunks of this data and took the Fourier transform to find the dominant frequency: http://www.maths.tcd.ie/~dwmalone/time/leap2012/#mains but I guess you could filter it and count crossings too? David.
BD
Bill Dailey
Sat, Nov 16, 2013 10:08 PM

There is no higher purpose actually.  I just fiddle.  This is how I relax.

On Sat, Nov 16, 2013 at 3:47 PM, Chris Albertson
albertson.chris@gmail.comwrote:

No, I meant the purpose of the whole thing.  Why are you measuring power
frequency?  Not why are you using a PIC.    How will the data be used, what
is the question driving the measurement?

On Sat, Nov 16, 2013 at 11:23 AM, Bill Dailey docdailey@gmail.com wrote:

My purpose is to do it with a picpet.  That's it.  So, that eliminates a
bunch of the options.  I can decouple the measurements from the pc clock
that way.

Doc

Sent from mobile

On Nov 16, 2013, at 11:26 AM, Chris Albertson <

wrote:

The signal is 120 volts.  You hardly need to amplify it.  Clip it with

a

diode to +- 9 volts so as not to blow up your serial port.  But I'd

use a

transformer for safety. The zero crossing detectors are built into the
RS232 interface.    You take advantage of the RS232 spec which has a

DCD

pin input of about +-9 volts that is already set up to find a leading

edge

of a pulse and cause a very low latency interrupt.  The system software
already will capture the time all inside a kernel level interrupt

handler.

The jitter turns out to be on the order of a single digit microseconds.
Good enough for measuring a 60Hz signal.

I guess if you want to see transients depends on the purpose of the
experiment.  Are you looking at local AC power quality or wanting to
measure the grid.  The grid is well monitored, just use FNET and you

get

real-time data for all of North America.  I think the reason for

measuring

it yourself is to see local power quality and things load switching

inside

your own building, that's transients.

The other way to measure AC with zero added equipment is to treat it as

an

audio signal and after reducing it to 1 volt run it into an audio

interface

And then use FFT.  This will let you see very small spikes and noise.

It

depends again on your purpose for doing this.

On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson <
magnus@rubidium.dyndns.org> wrote:

On 11/16/2013 09:52 AM, Chris Albertson wrote:
Your method tosses out a lot of data.  You can't see transients.

Ideally

rather then record a 1 second average you'd record the time of EVERY

zero

crossing.  It sounds like a lot of data but not really.  You only

record

32 bits 60 times each second.  That is 240 bytes per second.

But you want it filtered to avoid the transients. Those are really not
that interesting when you measure the grid.

Also, if you use the event trigger method you probably want to use an
amplifier to increase the slew-rate such that noise does not convert
into time jitter.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO

There is no higher purpose actually. I just fiddle. This is how I relax. On Sat, Nov 16, 2013 at 3:47 PM, Chris Albertson <albertson.chris@gmail.com>wrote: > No, I meant the purpose of the whole thing. Why are you measuring power > frequency? Not why are you using a PIC. How will the data be used, what > is the question driving the measurement? > > > On Sat, Nov 16, 2013 at 11:23 AM, Bill Dailey <docdailey@gmail.com> wrote: > > > My purpose is to do it with a picpet. That's it. So, that eliminates a > > bunch of the options. I can decouple the measurements from the pc clock > > that way. > > > > Doc > > > > Sent from mobile > > > > > On Nov 16, 2013, at 11:26 AM, Chris Albertson < > albertson.chris@gmail.com> > > wrote: > > > > > > The signal is 120 volts. You hardly need to amplify it. Clip it with > a > > > diode to +- 9 volts so as not to blow up your serial port. But I'd > use a > > > transformer for safety. The zero crossing detectors are built into the > > > RS232 interface. You take advantage of the RS232 spec which has a > DCD > > > pin input of about +-9 volts that is already set up to find a leading > > edge > > > of a pulse and cause a very low latency interrupt. The system software > > > already will capture the time all inside a kernel level interrupt > > handler. > > > > > > The jitter turns out to be on the order of a single digit microseconds. > > > Good enough for measuring a 60Hz signal. > > > > > > I guess if you want to see transients depends on the purpose of the > > > experiment. Are you looking at local AC power quality or wanting to > > > measure the grid. The grid is well monitored, just use FNET and you > get > > > real-time data for all of North America. I think the reason for > > measuring > > > it yourself is to see local power quality and things load switching > > inside > > > your own building, that's transients. > > > > > > > > > > > > The other way to measure AC with zero added equipment is to treat it as > > an > > > audio signal and after reducing it to 1 volt run it into an audio > > interface > > > And then use FFT. This will let you see very small spikes and noise. > > It > > > depends again on your purpose for doing this. > > > > > > > > > > > > > > > On Sat, Nov 16, 2013 at 1:18 AM, Magnus Danielson < > > > magnus@rubidium.dyndns.org> wrote: > > > > > >>> On 11/16/2013 09:52 AM, Chris Albertson wrote: > > >>> Your method tosses out a lot of data. You can't see transients. > > Ideally > > >>> rather then record a 1 second average you'd record the time of EVERY > > zero > > >>> crossing. It sounds like a lot of data but not really. You only > > record > > >>> 32 bits 60 times each second. That is 240 bytes per second. > > >> But you want it filtered to avoid the transients. Those are really not > > >> that interesting when you measure the grid. > > >> > > >> Also, if you use the event trigger method you probably want to use an > > >> amplifier to increase the slew-rate such that noise does not convert > > >> into time jitter. > > >> > > >> Cheers, > > >> Magnus > > >> _______________________________________________ > > >> time-nuts mailing list -- time-nuts@febo.com > > >> To unsubscribe, go to > > >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > > >> and follow the instructions there. > > > > > > > > > > > > -- > > > > > > Chris Albertson > > > Redondo Beach, California > > > _______________________________________________ > > > time-nuts mailing list -- time-nuts@febo.com > > > To unsubscribe, go to > > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > > > and follow the instructions there. > > _______________________________________________ > > time-nuts mailing list -- time-nuts@febo.com > > To unsubscribe, go to > > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > > and follow the instructions there. > > > > > > -- > > Chris Albertson > Redondo Beach, California > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Doc Bill Dailey KXØO
CH
Chuck Harris
Sat, Nov 16, 2013 11:49 PM

Only if the noise in question comes from the trigger electronics.

In the case of a 60Hz mains derived signal, most of the noise is
going to be riding on the signal, and will be amplified with your
gain stage.  A -delta amplitude noise signal will be zero when the
sine wave signal is at +delta.  That will be sometime other than
the actual zero crossing... which is phase noise.

-Chuck Harris

Magnus Danielson wrote:

On 11/16/2013 03:13 PM, Chuck Harris wrote:

Random noise always converts into time jitter.  It doesn't
matter how much you amplify the input signal, noise can push
the detected zero crossing wherever it wants to.

You are missing that you can alter how much trigger jitter you get.

Cheers,
Magnus

-Chuck Harris

Only if the noise in question comes from the trigger electronics. In the case of a 60Hz mains derived signal, most of the noise is going to be riding on the signal, and will be amplified with your gain stage. A -delta amplitude noise signal will be zero when the sine wave signal is at +delta. That will be sometime other than the actual zero crossing... which is phase noise. -Chuck Harris Magnus Danielson wrote: > On 11/16/2013 03:13 PM, Chuck Harris wrote: >> Random noise always converts into time jitter. It doesn't >> matter how much you amplify the input signal, noise can push >> the detected zero crossing wherever it wants to. > You are missing that you can alter how much trigger jitter you get. > > Cheers, > Magnus > >> >> -Chuck Harris
CS
Charles Steinmetz
Sun, Nov 17, 2013 12:54 AM

Chuck wrote:

In the case of a 60Hz mains derived signal, most of the noise is
going to be riding on the signal, and will be amplified with your
gain stage.

The potential evils of bandpass filters in a timing chain are well
known, but as long as you can accept the delay of a filter (or
correct for it, which should be trivial with a PIC or other uC), you
may be much further ahead with a noisy signal like the AC mains if
you use a sharp bandpass filter on the incoming 60 Hz then amplify &
clip the signal to increase the slew rate.  Active filters with fast,
quiet op-amps should do the job well.  For the lowest jitter, a
Collins-style multi-stage zero cross detector may be helpful.

Best regards,

Charles

Chuck wrote: >In the case of a 60Hz mains derived signal, most of the noise is >going to be riding on the signal, and will be amplified with your >gain stage. The potential evils of bandpass filters in a timing chain are well known, but as long as you can accept the delay of a filter (or correct for it, which should be trivial with a PIC or other uC), you may be much further ahead with a noisy signal like the AC mains if you use a sharp bandpass filter on the incoming 60 Hz then amplify & clip the signal to increase the slew rate. Active filters with fast, quiet op-amps should do the job well. For the lowest jitter, a Collins-style multi-stage zero cross detector may be helpful. Best regards, Charles
TV
Tom Van Baak
Sun, Nov 17, 2013 2:02 AM

Charles, et al.

I think we agree. Just to clarify...

I rely on no hardware and no software filters when I use a time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or sub-microsecond picPET. An electrical zero-crossing happens when it happens. If you "filter" you're just trying to change history: spikes are spikes; noise is noise; history is history. Deal with it. Record it, don't filter it away.

The beauty of the time-stamping method is that you capture any and all positive zero-crossings. If there is "noise" all it does is create unexpected and obvious artificial too-early or too-late samples -- which are trivial to analyze or eliminate in software.

Some call them "outliers" and ignore them. This is correct. However, if one "filters" or "averages" them, you give validity they may not deserve. Bogus data should be eliminated by logic, not attenuated with pseudo-analog filtering.

You can either focus on the signal, or the noise. That's two separate plots. An extraneous time-stamp happens to me a couple times a month; they are easy to spot and ignore. Similarly, a couple times a year I might miss a 60 Hz sample; these are also easy to spot and repair. For best time & frequency results, never "divide by =60"; instead "decimate by ~1 second".

/tvb

----- Original Message -----
From: "Charles Steinmetz" csteinmetz@yandex.com
To: "Discussion of precise time and frequency measurement" time-nuts@febo.com
Sent: Saturday, November 16, 2013 4:54 PM
Subject: Re: [time-nuts] Mains frequency

Chuck wrote:

In the case of a 60Hz mains derived signal, most of the noise is
going to be riding on the signal, and will be amplified with your
gain stage.

The potential evils of bandpass filters in a timing chain are well
known, but as long as you can accept the delay of a filter (or
correct for it, which should be trivial with a PIC or other uC), you
may be much further ahead with a noisy signal like the AC mains if
you use a sharp bandpass filter on the incoming 60 Hz then amplify &
clip the signal to increase the slew rate.  Active filters with fast,
quiet op-amps should do the job well.  For the lowest jitter, a
Collins-style multi-stage zero cross detector may be helpful.

Best regards,

Charles

Charles, et al. I think we agree. Just to clarify... I rely on no hardware and no software filters when I use a time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or sub-microsecond picPET. An electrical zero-crossing happens when it happens. If you "filter" you're just trying to change history: spikes are spikes; noise is noise; history is history. Deal with it. Record it, don't filter it away. The beauty of the time-stamping method is that you capture any and all positive zero-crossings. If there is "noise" all it does is create unexpected and obvious artificial too-early or too-late samples -- which are trivial to analyze or eliminate in software. Some call them "outliers" and ignore them. This is correct. However, if one "filters" or "averages" them, you give validity they may not deserve. Bogus data should be eliminated by *logic*, not attenuated with pseudo-analog *filtering*. You can either focus on the signal, or the noise. That's two separate plots. An extraneous time-stamp happens to me a couple times a month; they are easy to spot and ignore. Similarly, a couple times a year I might miss a 60 Hz sample; these are also easy to spot and repair. For best time & frequency results, never "divide by =60"; instead "decimate by ~1 second". /tvb ----- Original Message ----- From: "Charles Steinmetz" <csteinmetz@yandex.com> To: "Discussion of precise time and frequency measurement" <time-nuts@febo.com> Sent: Saturday, November 16, 2013 4:54 PM Subject: Re: [time-nuts] Mains frequency > Chuck wrote: > >>In the case of a 60Hz mains derived signal, most of the noise is >>going to be riding on the signal, and will be amplified with your >>gain stage. > > The potential evils of bandpass filters in a timing chain are well > known, but as long as you can accept the delay of a filter (or > correct for it, which should be trivial with a PIC or other uC), you > may be much further ahead with a noisy signal like the AC mains if > you use a sharp bandpass filter on the incoming 60 Hz then amplify & > clip the signal to increase the slew rate. Active filters with fast, > quiet op-amps should do the job well. For the lowest jitter, a > Collins-style multi-stage zero cross detector may be helpful. > > Best regards, > > Charles
MD
Magnus Danielson
Sun, Nov 17, 2013 2:26 AM

Tom,

On 11/17/2013 03:02 AM, Tom Van Baak wrote:

Charles, et al.

I think we agree. Just to clarify...

I rely on no hardware and no software filters when I use a time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or sub-microsecond picPET. An electrical zero-crossing happens when it happens. If you "filter" you're just trying to change history: spikes are spikes; noise is noise; history is history. Deal with it. Record it, don't filter it away.

The beauty of the time-stamping method is that you capture any and all positive zero-crossings. If there is "noise" all it does is create unexpected and obvious artificial too-early or too-late samples -- which are trivial to analyze or eliminate in software.

Some call them "outliers" and ignore them. This is correct. However, if one "filters" or "averages" them, you give validity they may not deserve. Bogus data should be eliminated by logic, not attenuated with pseudo-analog filtering.

You can either focus on the signal, or the noise. That's two separate plots. An extraneous time-stamp happens to me a couple times a month; they are easy to spot and ignore. Similarly, a couple times a year I might miss a 60 Hz sample; these are also easy to spot and repair. For best time & frequency results, never "divide by =60"; instead "decimate by ~1 second".

Standard wide-bandwidth counters isn't really ideal for signals like this.

When you measure the mains signal, nominally 60 Hz in this case, spikes
etc. is noise which is local and not of interest when comparing over a
large area. Inter-area oscillations have much slower properties.
If you go the time-stamping way, you should remove such noise.

Removing or padding over it by logic will mean dropping data, which is
not helpful.

Turns out that professional gear for this does not do time-stamping in
this regard. Rather, they I-Q demodulate the signal with a reference
signal at the nominal rate, low-pass filter it and pay attention to
details of filtering like group-delay and compensation thereof. It's a
rather wise approach for the type of conditions you have.

Cheers,
Magnus

Tom, On 11/17/2013 03:02 AM, Tom Van Baak wrote: > Charles, et al. > > I think we agree. Just to clarify... > > I rely on no hardware and no software filters when I use a time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or sub-microsecond picPET. An electrical zero-crossing happens when it happens. If you "filter" you're just trying to change history: spikes are spikes; noise is noise; history is history. Deal with it. Record it, don't filter it away. > > The beauty of the time-stamping method is that you capture any and all positive zero-crossings. If there is "noise" all it does is create unexpected and obvious artificial too-early or too-late samples -- which are trivial to analyze or eliminate in software. > > Some call them "outliers" and ignore them. This is correct. However, if one "filters" or "averages" them, you give validity they may not deserve. Bogus data should be eliminated by *logic*, not attenuated with pseudo-analog *filtering*. > > You can either focus on the signal, or the noise. That's two separate plots. An extraneous time-stamp happens to me a couple times a month; they are easy to spot and ignore. Similarly, a couple times a year I might miss a 60 Hz sample; these are also easy to spot and repair. For best time & frequency results, never "divide by =60"; instead "decimate by ~1 second". Standard wide-bandwidth counters isn't really ideal for signals like this. When you measure the mains signal, nominally 60 Hz in this case, spikes etc. is noise which is local and not of interest when comparing over a large area. Inter-area oscillations have much slower properties. If you go the time-stamping way, you *should* remove such noise. Removing or padding over it by logic will mean dropping data, which is not helpful. Turns out that professional gear for this does not do time-stamping in this regard. Rather, they I-Q demodulate the signal with a reference signal at the nominal rate, low-pass filter it and pay attention to details of filtering like group-delay and compensation thereof. It's a rather wise approach for the type of conditions you have. Cheers, Magnus
CA
Chris Albertson
Sun, Nov 17, 2013 2:33 AM

Again, why are you measuring the AC line?  I'd think maybe to measure the
noise that is on it.  The fundamental freq. changes second by second.
It's not a clean 60Hz my any means.  The rate of frequency change is one
thing you'd like to measure

I was just watching a minute ago and can see a 0.01Hz/second drift.  It is
likely MUCH worse as what I was watching is filtered over second

On Sat, Nov 16, 2013 at 4:54 PM, Charles Steinmetz csteinmetz@yandex.comwrote:

Chuck wrote:

In the case of a 60Hz mains derived signal, most of the noise is

going to be riding on the signal, and will be amplified with your
gain stage.

The potential evils of bandpass filters in a timing chain are well known,
but as long as you can accept the delay of a filter (or correct for it,
which should be trivial with a PIC or other uC), you may be much further
ahead with a noisy signal like the AC mains if you use a sharp bandpass
filter on the incoming 60 Hz then amplify & clip the signal to increase the
slew rate.  Active filters with fast, quiet op-amps should do the job well.
For the lowest jitter, a Collins-style multi-stage zero cross detector may
be helpful.

Best regards,

Charles


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/
mailman/listinfo/time-nuts
and follow the instructions there.

--

Chris Albertson
Redondo Beach, California

Again, why are you measuring the AC line? I'd think maybe to measure the noise that is on it. The fundamental freq. changes second by second. It's not a clean 60Hz my any means. The rate of frequency change is one thing you'd like to measure I was just watching a minute ago and can see a 0.01Hz/second drift. It is likely MUCH worse as what I was watching is filtered over second On Sat, Nov 16, 2013 at 4:54 PM, Charles Steinmetz <csteinmetz@yandex.com>wrote: > Chuck wrote: > > In the case of a 60Hz mains derived signal, most of the noise is >> going to be riding on the signal, and will be amplified with your >> gain stage. >> > > The potential evils of bandpass filters in a timing chain are well known, > but as long as you can accept the delay of a filter (or correct for it, > which should be trivial with a PIC or other uC), you may be much further > ahead with a noisy signal like the AC mains if you use a sharp bandpass > filter on the incoming 60 Hz then amplify & clip the signal to increase the > slew rate. Active filters with fast, quiet op-amps should do the job well. > For the lowest jitter, a Collins-style multi-stage zero cross detector may > be helpful. > > Best regards, > > Charles > > > > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/ > mailman/listinfo/time-nuts > and follow the instructions there. > -- Chris Albertson Redondo Beach, California
MD
Magnus Danielson
Sun, Nov 17, 2013 2:47 AM

On 11/17/2013 03:33 AM, Chris Albertson wrote:

Again, why are you measuring the AC line?  I'd think maybe to measure the
noise that is on it.  The fundamental freq. changes second by second.
It's not a clean 60Hz my any means.  The rate of frequency change is one
thing you'd like to measure

I was just watching a minute ago and can see a 0.01Hz/second drift.  It is
likely MUCH worse as what I was watching is filtered over second

The phase of it tells you a lot about the powergrid, especially when you
collect data over the full power-grid and at sufficiently high rate.

Cheers,
Magnus

On 11/17/2013 03:33 AM, Chris Albertson wrote: > Again, why are you measuring the AC line? I'd think maybe to measure the > noise that is on it. The fundamental freq. changes second by second. > It's not a clean 60Hz my any means. The rate of frequency change is one > thing you'd like to measure > > I was just watching a minute ago and can see a 0.01Hz/second drift. It is > likely MUCH worse as what I was watching is filtered over second The phase of it tells you a lot about the powergrid, especially when you collect data over the full power-grid and at sufficiently high rate. Cheers, Magnus
TV
Tom Van Baak
Sun, Nov 17, 2013 2:53 AM

When you measure the mains signal, nominally 60 Hz in this case, spikes
etc. is noise which is local and not of interest when comparing over a
large area. Inter-area oscillations have much slower properties.
If you go the time-stamping way, you should remove such noise.

Removing or padding over it by logic will mean dropping data, which is
not helpful.

A time-stamping counter never drops data; instead you apply logic to drop noise when necessary.

Turns out that professional gear for this does not do time-stamping in
this regard. Rather, they I-Q demodulate the signal with a reference
signal at the nominal rate, low-pass filter it and pay attention to
details of filtering like group-delay and compensation thereof. It's a
rather wise approach for the type of conditions you have.

I'd be happy to compare "professional gear" with a time-stamping counter. I have two or three years of data to show 60 Hz time-stamping works perfectly. Not to say your professional gear might also. But a zero-crossing counter never misses a cycle; you can set the s/w bandwidth just as you can set an IQ hardware bandwidth.  Both assume some reasonable limit of mains df/f/dt. You can either do it with a fancy $100 to $1000 reference signal generator + PLL or FLL + IQ detector + professional box -- or with a $1 PIC and $0 s/w.

/tvb

> When you measure the mains signal, nominally 60 Hz in this case, spikes > etc. is noise which is local and not of interest when comparing over a > large area. Inter-area oscillations have much slower properties. > If you go the time-stamping way, you *should* remove such noise. > > Removing or padding over it by logic will mean dropping data, which is > not helpful. A time-stamping counter never drops *data*; instead you apply logic to drop *noise* when necessary. > Turns out that professional gear for this does not do time-stamping in > this regard. Rather, they I-Q demodulate the signal with a reference > signal at the nominal rate, low-pass filter it and pay attention to > details of filtering like group-delay and compensation thereof. It's a > rather wise approach for the type of conditions you have. I'd be happy to compare "professional gear" with a time-stamping counter. I have two or three years of data to show 60 Hz time-stamping works perfectly. Not to say your professional gear might also. But a zero-crossing counter never misses a cycle; you can set the s/w bandwidth just as you can set an IQ hardware bandwidth. Both assume some reasonable limit of mains df/f/dt. You can either do it with a fancy $100 to $1000 reference signal generator + PLL or FLL + IQ detector + professional box -- or with a $1 PIC and $0 s/w. /tvb
TV
Tom Van Baak
Sun, Nov 17, 2013 3:17 AM

Again, why are you measuring the AC line?  I'd think maybe to measure the
noise that is on it.  The fundamental freq. changes second by second.
It's not a clean 60Hz my any means.  The rate of frequency change is one
thing you'd like to measure

I was just watching a minute ago and can see a 0.01Hz/second drift.  It is
likely MUCH worse as what I was watching is filtered over second

Chris,

No, forget the noise (it's actually quite clean: look at it sometime).

We measure mains because we can.

We also measure it because millions of wall-clocks are based on mains frequency; it was the original "GPSDO".

We measure it because its phase plot, frequency histogram, and ADEV plot are really quite interesting.

We measure it because Seattle, WA (tvb) and New Mexico (Kevin) are both on the same grid and mutually agree to 10 microseconds (!) over an hour even though they can both wander by many seconds relative to UTC. It's a textbook example of common view time transfer. See also:
http://leapsecond.com/pages/mains/
http://leapsecond.com/pages/ac-detect/

You too can join the mains party. Measure it with your own method, or a fancy TrueTime time/frequency deviation meter (TFDM) or use something simple like a picPET (http://www.leapsecond.com/pic/picpet.htm) or Arduino or even a NTP/Linux/serial DCD pin hack.

/tvb

> Again, why are you measuring the AC line? I'd think maybe to measure the > noise that is on it. The fundamental freq. changes second by second. > It's not a clean 60Hz my any means. The rate of frequency change is one > thing you'd like to measure > > I was just watching a minute ago and can see a 0.01Hz/second drift. It is > likely MUCH worse as what I was watching is filtered over second Chris, No, forget the noise (it's actually quite clean: look at it sometime). We measure mains because we can. We also measure it because millions of wall-clocks are based on mains frequency; it was the original "GPSDO". We measure it because its phase plot, frequency histogram, and ADEV plot are really quite interesting. We measure it because Seattle, WA (tvb) and New Mexico (Kevin) are both on the same grid and mutually agree to 10 microseconds (!) over an hour even though they can both wander by many seconds relative to UTC. It's a textbook example of common view time transfer. See also: http://leapsecond.com/pages/mains/ http://leapsecond.com/pages/ac-detect/ You too can join the mains party. Measure it with your own method, or a fancy TrueTime time/frequency deviation meter (TFDM) or use something simple like a picPET (http://www.leapsecond.com/pic/picpet.htm) or Arduino or even a NTP/Linux/serial DCD pin hack. /tvb
DJ
Didier Juges
Sun, Nov 17, 2013 3:24 AM

For a non Time-Nuts application, I needed a narrow bandpass filter that would provide essentially zero phase shift (no more than 10 or 20uS was desired) over a frequency range of 55 to 65 Hz while providing useful reduction of the harmonics, particularly in the range of 400 to 1kHz. This was to filter the line voltage. I needed an output that was  a clean sine wave but with essentially no phase or amplitude error compared to the input signal, even when the input signal changed in frequency.
Of course, there is no "conventional" filter topology that will provide zero phase shift over a range of frequency, you will be lucky to find one that provides zero phase shift at ONE frequency. I knew the switched capacitor filter could be set to provide zero phase shift near the center frequency, but the phase shift would change rapidly when the input frequency changed, like any other filter.
I came across the LTC1060 and I found out that when driving its clock from a PLL that multiplies the line frequency by the proper factor (50 or 100 for the LTC1060), a single potentiometer can then be used to adjust the phase shift to zero nominally, and the phase shift remains below a few uS over the range I was interested in.

Being a switched capacitor filter, it can be made as narrow as desired without affecting the other characteristics too much.

Reading this thread, I just realized that this filter would be very useful to filter the 60Hz before feeding a counter for the purpose of measuring the line frequency and phase without being too much affected by noise and other disturbances.

Didier KO4BB

Charles Steinmetz csteinmetz@yandex.com wrote:

Chuck wrote:

In the case of a 60Hz mains derived signal, most of the noise is
going to be riding on the signal, and will be amplified with your
gain stage.

The potential evils of bandpass filters in a timing chain are well
known, but as long as you can accept the delay of a filter (or
correct for it, which should be trivial with a PIC or other uC), you
may be much further ahead with a noisy signal like the AC mains if
you use a sharp bandpass filter on the incoming 60 Hz then amplify &
clip the signal to increase the slew rate.  Active filters with fast,
quiet op-amps should do the job well.  For the lowest jitter, a
Collins-style multi-stage zero cross detector may be helpful.

Best regards,

Charles


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other things.

For a non Time-Nuts application, I needed a narrow bandpass filter that would provide essentially zero phase shift (no more than 10 or 20uS was desired) over a frequency range of 55 to 65 Hz while providing useful reduction of the harmonics, particularly in the range of 400 to 1kHz. This was to filter the line voltage. I needed an output that was a clean sine wave but with essentially no phase or amplitude error compared to the input signal, even when the input signal changed in frequency. Of course, there is no "conventional" filter topology that will provide zero phase shift over a range of frequency, you will be lucky to find one that provides zero phase shift at ONE frequency. I knew the switched capacitor filter could be set to provide zero phase shift near the center frequency, but the phase shift would change rapidly when the input frequency changed, like any other filter. I came across the LTC1060 and I found out that when driving its clock from a PLL that multiplies the line frequency by the proper factor (50 or 100 for the LTC1060), a single potentiometer can then be used to adjust the phase shift to zero nominally, and the phase shift remains below a few uS over the range I was interested in. Being a switched capacitor filter, it can be made as narrow as desired without affecting the other characteristics too much. Reading this thread, I just realized that this filter would be very useful to filter the 60Hz before feeding a counter for the purpose of measuring the line frequency and phase without being too much affected by noise and other disturbances. Didier KO4BB Charles Steinmetz <csteinmetz@yandex.com> wrote: >Chuck wrote: > >>In the case of a 60Hz mains derived signal, most of the noise is >>going to be riding on the signal, and will be amplified with your >>gain stage. > >The potential evils of bandpass filters in a timing chain are well >known, but as long as you can accept the delay of a filter (or >correct for it, which should be trivial with a PIC or other uC), you >may be much further ahead with a noisy signal like the AC mains if >you use a sharp bandpass filter on the incoming 60 Hz then amplify & >clip the signal to increase the slew rate. Active filters with fast, >quiet op-amps should do the job well. For the lowest jitter, a >Collins-style multi-stage zero cross detector may be helpful. > >Best regards, > >Charles > > > >_______________________________________________ >time-nuts mailing list -- time-nuts@febo.com >To unsubscribe, go to >https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >and follow the instructions there. -- Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other things.
BD
Bill Dailey
Sun, Nov 17, 2013 3:27 AM

Does an ac transformer hurt me?  I was looking for that dang megohm page when I started this.  Couldn't find it so I used a transformer.

Doc

Sent from my iPad

On Nov 16, 2013, at 9:17 PM, "Tom Van Baak" tvb@LeapSecond.com wrote:

Again, why are you measuring the AC line?  I'd think maybe to measure the
noise that is on it.  The fundamental freq. changes second by second.
It's not a clean 60Hz my any means.  The rate of frequency change is one
thing you'd like to measure

I was just watching a minute ago and can see a 0.01Hz/second drift.  It is
likely MUCH worse as what I was watching is filtered over second

Chris,

No, forget the noise (it's actually quite clean: look at it sometime).

We measure mains because we can.

We also measure it because millions of wall-clocks are based on mains frequency; it was the original "GPSDO".

We measure it because its phase plot, frequency histogram, and ADEV plot are really quite interesting.

We measure it because Seattle, WA (tvb) and New Mexico (Kevin) are both on the same grid and mutually agree to 10 microseconds (!) over an hour even though they can both wander by many seconds relative to UTC. It's a textbook example of common view time transfer. See also:
http://leapsecond.com/pages/mains/
http://leapsecond.com/pages/ac-detect/

You too can join the mains party. Measure it with your own method, or a fancy TrueTime time/frequency deviation meter (TFDM) or use something simple like a picPET (http://www.leapsecond.com/pic/picpet.htm) or Arduino or even a NTP/Linux/serial DCD pin hack.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Does an ac transformer hurt me? I was looking for that dang megohm page when I started this. Couldn't find it so I used a transformer. Doc Sent from my iPad On Nov 16, 2013, at 9:17 PM, "Tom Van Baak" <tvb@LeapSecond.com> wrote: >> Again, why are you measuring the AC line? I'd think maybe to measure the >> noise that is on it. The fundamental freq. changes second by second. >> It's not a clean 60Hz my any means. The rate of frequency change is one >> thing you'd like to measure >> >> I was just watching a minute ago and can see a 0.01Hz/second drift. It is >> likely MUCH worse as what I was watching is filtered over second > > Chris, > > No, forget the noise (it's actually quite clean: look at it sometime). > > We measure mains because we can. > > We also measure it because millions of wall-clocks are based on mains frequency; it was the original "GPSDO". > > We measure it because its phase plot, frequency histogram, and ADEV plot are really quite interesting. > > We measure it because Seattle, WA (tvb) and New Mexico (Kevin) are both on the same grid and mutually agree to 10 microseconds (!) over an hour even though they can both wander by many seconds relative to UTC. It's a textbook example of common view time transfer. See also: > http://leapsecond.com/pages/mains/ > http://leapsecond.com/pages/ac-detect/ > > You too can join the mains party. Measure it with your own method, or a fancy TrueTime time/frequency deviation meter (TFDM) or use something simple like a picPET (http://www.leapsecond.com/pic/picpet.htm) or Arduino or even a NTP/Linux/serial DCD pin hack. > > /tvb > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
DJ
Didier Juges
Sun, Nov 17, 2013 3:32 AM

"Turns out that professional gear for this does not do time-stamping in
this regard. Rather, they I-Q demodulate the signal with a reference
signal at the nominal rate, low-pass filter it and pay attention to
details of filtering like group-delay and compensation thereof."

It makes sense to me. That way, you use the entire signal instead of just the zero crossing.
You know that the signal is generated as a sine wave. Therefore, essentially you synthesize a local sine wave that is a best fit to the input signal and you measure the zero crossings of the synthesized signal.

Didier KO4BB

Magnus Danielson magnus@rubidium.dyndns.org wrote:

Tom,

On 11/17/2013 03:02 AM, Tom Van Baak wrote:

Charles, et al.

I think we agree. Just to clarify...

I rely on no hardware and no software filters when I use a

time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or
sub-microsecond picPET. An electrical zero-crossing happens when it
happens. If you "filter" you're just trying to change history: spikes
are spikes; noise is noise; history is history. Deal with it. Record
it, don't filter it away.

The beauty of the time-stamping method is that you capture any and

all positive zero-crossings. If there is "noise" all it does is create
unexpected and obvious artificial too-early or too-late samples --
which are trivial to analyze or eliminate in software.

Some call them "outliers" and ignore them. This is correct. However,

if one "filters" or "averages" them, you give validity they may not
deserve. Bogus data should be eliminated by logic, not attenuated
with pseudo-analog filtering.

You can either focus on the signal, or the noise. That's two separate

plots. An extraneous time-stamp happens to me a couple times a month;
they are easy to spot and ignore. Similarly, a couple times a year I
might miss a 60 Hz sample; these are also easy to spot and repair. For
best time & frequency results, never "divide by =60"; instead "decimate
by ~1 second".
Standard wide-bandwidth counters isn't really ideal for signals like
this.

When you measure the mains signal, nominally 60 Hz in this case, spikes
etc. is noise which is local and not of interest when comparing over a
large area. Inter-area oscillations have much slower properties.
If you go the time-stamping way, you should remove such noise.

Removing or padding over it by logic will mean dropping data, which is
not helpful.

Turns out that professional gear for this does not do time-stamping in
this regard. Rather, they I-Q demodulate the signal with a reference
signal at the nominal rate, low-pass filter it and pay attention to
details of filtering like group-delay and compensation thereof. It's a
rather wise approach for the type of conditions you have.

Cheers,
Magnus


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other things.

"Turns out that professional gear for this does not do time-stamping in this regard. Rather, they I-Q demodulate the signal with a reference signal at the nominal rate, low-pass filter it and pay attention to details of filtering like group-delay and compensation thereof." It makes sense to me. That way, you use the entire signal instead of just the zero crossing. You know that the signal is generated as a sine wave. Therefore, essentially you synthesize a local sine wave that is a best fit to the input signal and you measure the zero crossings of the synthesized signal. Didier KO4BB Magnus Danielson <magnus@rubidium.dyndns.org> wrote: >Tom, > >On 11/17/2013 03:02 AM, Tom Van Baak wrote: >> Charles, et al. >> >> I think we agree. Just to clarify... >> >> I rely on no hardware and no software filters when I use a >time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or >sub-microsecond picPET. An electrical zero-crossing happens when it >happens. If you "filter" you're just trying to change history: spikes >are spikes; noise is noise; history is history. Deal with it. Record >it, don't filter it away. >> >> The beauty of the time-stamping method is that you capture any and >all positive zero-crossings. If there is "noise" all it does is create >unexpected and obvious artificial too-early or too-late samples -- >which are trivial to analyze or eliminate in software. >> >> Some call them "outliers" and ignore them. This is correct. However, >if one "filters" or "averages" them, you give validity they may not >deserve. Bogus data should be eliminated by *logic*, not attenuated >with pseudo-analog *filtering*. >> >> You can either focus on the signal, or the noise. That's two separate >plots. An extraneous time-stamp happens to me a couple times a month; >they are easy to spot and ignore. Similarly, a couple times a year I >might miss a 60 Hz sample; these are also easy to spot and repair. For >best time & frequency results, never "divide by =60"; instead "decimate >by ~1 second". >Standard wide-bandwidth counters isn't really ideal for signals like >this. > >When you measure the mains signal, nominally 60 Hz in this case, spikes >etc. is noise which is local and not of interest when comparing over a >large area. Inter-area oscillations have much slower properties. >If you go the time-stamping way, you *should* remove such noise. > >Removing or padding over it by logic will mean dropping data, which is >not helpful. > >Turns out that professional gear for this does not do time-stamping in >this regard. Rather, they I-Q demodulate the signal with a reference >signal at the nominal rate, low-pass filter it and pay attention to >details of filtering like group-delay and compensation thereof. It's a >rather wise approach for the type of conditions you have. > >Cheers, >Magnus >_______________________________________________ >time-nuts mailing list -- time-nuts@febo.com >To unsubscribe, go to >https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >and follow the instructions there. -- Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other things.
CS
Charles Steinmetz
Sun, Nov 17, 2013 3:35 AM

tvb wrote:

I think we agree. Just to clarify...

I rely on no hardware and no software filters when I use a
time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or
sub-microsecond picPET. An electrical zero-crossing happens when it
happens. If you "filter" you're just trying to change history:
spikes are spikes; noise is noise; history is history. Deal with it.
Record it, don't filter it away.

Well, it depends on what one wants to investigate.  The "naked"
history one captures with no filtering may not be the cleanest
history available of the phenomenon under investigation.  Except in
unusual circumstances, mains voltage is generated by massive rotating
machinery -- so anything fast that happens on your incoming mains
voltage is not a reflection of the grid frequency.  If what you want
to know is the grid frequency over time (vector sum of the rotational
velocity of the various generators on the grid, as seen from your
location), a filtered and limited signal may (probably will) provide
the best assessment.  Note that local zero crossings are only a proxy
for grid frequency to begin with -- and not a very good one,
specifically because of the high noise level.  Of course, you can
always filter in software if you time-stamp each zero cross in all
its naked glory, but removing the noise prior to time-stamping is
often preferable to digitally processing a noisy capture.

Put another way, the massive rotating machinery that generates the
mains voltage can only change the zero cross of the grid by a tiny
amount from one cycle to the next.  If a data capture method shows
cycle-to-cycle jitter that is significantly greater than this amount,
the increase cannot be due to the generators, it can only be due to
noise.  If one's interest is the grid frequency, removing this noise
prior to time-stamping can only help.

Note that I'm not talking about a filter Q in the millions -- I'd
probably be inclined to use a linear-phase filter with several Hz
bandwidth, after a more rigorous analysis of the application.

You can either focus on the signal, or the noise. That's two separate plots.

Agreed.  If you are investigating incidental noise on the mains
rather than the grid frequency, then the signal you capture needs to
be at least as broadband as the noise in which you are interested.

Since I do not use the actual local mains zero crossings for anything
(other than electronically switching loads on at zero voltage and off
at zero current, where absolute timing is irrelevant), I'm not sure
why one might be interested in characterizing them.  OTOH, since I do
have equipment that responds to the grid frequency, I can see
practical utility in characterizing that.  Hence my suggestion to filter.

Best regards,

Charles

tvb wrote: >I think we agree. Just to clarify... > >I rely on no hardware and no software filters when I use a >time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or >sub-microsecond picPET. An electrical zero-crossing happens when it >happens. If you "filter" you're just trying to change history: >spikes are spikes; noise is noise; history is history. Deal with it. >Record it, don't filter it away. Well, it depends on what one wants to investigate. The "naked" history one captures with no filtering may not be the cleanest history available of the phenomenon under investigation. Except in unusual circumstances, mains voltage is generated by massive rotating machinery -- so anything fast that happens on your incoming mains voltage is not a reflection of the grid frequency. If what you want to know is the grid frequency over time (vector sum of the rotational velocity of the various generators on the grid, as seen from your location), a filtered and limited signal may (probably will) provide the best assessment. Note that local zero crossings are only a proxy for grid frequency to begin with -- and not a very good one, specifically because of the high noise level. Of course, you can always filter in software if you time-stamp each zero cross in all its naked glory, but removing the noise prior to time-stamping is often preferable to digitally processing a noisy capture. Put another way, the massive rotating machinery that generates the mains voltage can only change the zero cross of the grid by a tiny amount from one cycle to the next. If a data capture method shows cycle-to-cycle jitter that is significantly greater than this amount, the increase cannot be due to the generators, it can only be due to noise. If one's interest is the grid frequency, removing this noise prior to time-stamping can only help. Note that I'm not talking about a filter Q in the millions -- I'd probably be inclined to use a linear-phase filter with several Hz bandwidth, after a more rigorous analysis of the application. >You can either focus on the signal, or the noise. That's two separate plots. Agreed. If you are investigating incidental noise on the mains rather than the grid frequency, then the signal you capture needs to be at least as broadband as the noise in which you are interested. Since I do not use the actual local mains zero crossings for anything (other than electronically switching loads on at zero voltage and off at zero current, where absolute timing is irrelevant), I'm not sure why one might be interested in characterizing them. OTOH, since I do have equipment that responds to the grid frequency, I can see practical utility in characterizing that. Hence my suggestion to filter. Best regards, Charles
BD
Bill Dailey
Sun, Nov 17, 2013 3:49 AM

This resonates with me somewhat since I used to run nuclear power plants and operate the actual turbines.  It does seem that the time interval measurements have much more jitter than I would expect.  I suspect the thousands of turbines phase locked may introduce all kinds of very subtle variations.  I do know when you put a submarine turbine on shore power (grid). You no longer have to control speed... The grid does that for you.

Sent from my iPad

On Nov 16, 2013, at 9:35 PM, Charles Steinmetz csteinmetz@yandex.com wrote:

tvb wrote:

I think we agree. Just to clarify...

I rely on no hardware and no software filters when I use a time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or sub-microsecond picPET. An electrical zero-crossing happens when it happens. If you "filter" you're just trying to change history: spikes are spikes; noise is noise; history is history. Deal with it. Record it, don't filter it away.

Well, it depends on what one wants to investigate.  The "naked" history one captures with no filtering may not be the cleanest history available of the phenomenon under investigation.  Except in unusual circumstances, mains voltage is generated by massive rotating machinery -- so anything fast that happens on your incoming mains voltage is not a reflection of the grid frequency.  If what you want to know is the grid frequency over time (vector sum of the rotational velocity of the various generators on the grid, as seen from your location), a filtered and limited signal may (probably will) provide the best assessment.  Note that local zero crossings are only a proxy for grid frequency to begin with -- and not a very good one, specifically because of the high noise level.  Of course, you can always filter in software if you time-stamp each zero cross in all its naked glory, but removing the noise prior to time-stamping is often preferable to digitally processing a noisy capture.

Put another way, the massive rotating machinery that generates the mains voltage can only change the zero cross of the grid by a tiny amount from one cycle to the next.  If a data capture method shows cycle-to-cycle jitter that is significantly greater than this amount, the increase cannot be due to the generators, it can only be due to noise.  If one's interest is the grid frequency, removing this noise prior to time-stamping can only help.

Note that I'm not talking about a filter Q in the millions -- I'd probably be inclined to use a linear-phase filter with several Hz bandwidth, after a more rigorous analysis of the application.

You can either focus on the signal, or the noise. That's two separate plots.

Agreed.  If you are investigating incidental noise on the mains rather than the grid frequency, then the signal you capture needs to be at least as broadband as the noise in which you are interested.

Since I do not use the actual local mains zero crossings for anything (other than electronically switching loads on at zero voltage and off at zero current, where absolute timing is irrelevant), I'm not sure why one might be interested in characterizing them.  OTOH, since I do have equipment that responds to the grid frequency, I can see practical utility in characterizing that.  Hence my suggestion to filter.

Best regards,

Charles


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

This resonates with me somewhat since I used to run nuclear power plants and operate the actual turbines. It does seem that the time interval measurements have much more jitter than I would expect. I suspect the thousands of turbines phase locked may introduce all kinds of very subtle variations. I do know when you put a submarine turbine on shore power (grid). You no longer have to control speed... The grid does that for you. Sent from my iPad > On Nov 16, 2013, at 9:35 PM, Charles Steinmetz <csteinmetz@yandex.com> wrote: > > tvb wrote: > >> I think we agree. Just to clarify... >> >> I rely on no hardware and no software filters when I use a time-stamping counter such as a sub-nanosecond Pendulum CNT-9x or sub-microsecond picPET. An electrical zero-crossing happens when it happens. If you "filter" you're just trying to change history: spikes are spikes; noise is noise; history is history. Deal with it. Record it, don't filter it away. > > Well, it depends on what one wants to investigate. The "naked" history one captures with no filtering may not be the cleanest history available of the phenomenon under investigation. Except in unusual circumstances, mains voltage is generated by massive rotating machinery -- so anything fast that happens on your incoming mains voltage is not a reflection of the grid frequency. If what you want to know is the grid frequency over time (vector sum of the rotational velocity of the various generators on the grid, as seen from your location), a filtered and limited signal may (probably will) provide the best assessment. Note that local zero crossings are only a proxy for grid frequency to begin with -- and not a very good one, specifically because of the high noise level. Of course, you can always filter in software if you time-stamp each zero cross in all its naked glory, but removing the noise prior to time-stamping is often preferable to digitally processing a noisy capture. > > Put another way, the massive rotating machinery that generates the mains voltage can only change the zero cross of the grid by a tiny amount from one cycle to the next. If a data capture method shows cycle-to-cycle jitter that is significantly greater than this amount, the increase cannot be due to the generators, it can only be due to noise. If one's interest is the grid frequency, removing this noise prior to time-stamping can only help. > > Note that I'm not talking about a filter Q in the millions -- I'd probably be inclined to use a linear-phase filter with several Hz bandwidth, after a more rigorous analysis of the application. > >> You can either focus on the signal, or the noise. That's two separate plots. > > Agreed. If you are investigating incidental noise on the mains rather than the grid frequency, then the signal you capture needs to be at least as broadband as the noise in which you are interested. > > Since I do not use the actual local mains zero crossings for anything (other than electronically switching loads on at zero voltage and off at zero current, where absolute timing is irrelevant), I'm not sure why one might be interested in characterizing them. OTOH, since I do have equipment that responds to the grid frequency, I can see practical utility in characterizing that. Hence my suggestion to filter. > > Best regards, > > Charles > > > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BH
Bill Hawkins
Sun, Nov 17, 2013 5:46 PM

You can get some idea of industrial productivity if you can estimate
and remove non-industrial loads, perhaps by comparing weekends to
work weeks.  The dip during working hours and the rise at 4-5 AM are
proportional to the total power used, for the same generating
capacity.

The business of making up lost cycles on a daily business is not
easy for utilities. A year or two ago they proposed to let the
system float in order to eliminate failures caused by catching up.
Fortunately for timenuts, the proposal did not become practice.

Bill Hawkins

St. Paul: Money is the root of all evil.
Ben Franklin: Time is money.
Ergo - Time is the root of all evil.

-----Original Message-----
From: Tom Van Baak
Sent: Saturday, November 16, 2013 9:17 PM

---%<---

We measure mains because we can.

We also measure it because millions of wall-clocks are based on mains
frequency; it was the original "GPSDO".

We measure it because its phase plot, frequency histogram, and ADEV plot
are really quite interesting.

We measure it because Seattle, WA (tvb) and New Mexico (Kevin) are both
on the same grid and mutually agree to 10 microseconds (!) over an hour
even though they can both wander by many seconds relative to UTC. It's a
textbook example of common view time transfer. See also:
http://leapsecond.com/pages/mains/
http://leapsecond.com/pages/ac-detect/

You too can join the mains party. Measure it with your own method, or a
fancy TrueTime time/frequency deviation meter (TFDM) or use something
simple like a picPET (http://www.leapsecond.com/pic/picpet.htm) or
Arduino or even a NTP/Linux/serial DCD pin hack.

/tvb

You can get some idea of industrial productivity if you can estimate and remove non-industrial loads, perhaps by comparing weekends to work weeks. The dip during working hours and the rise at 4-5 AM are proportional to the total power used, for the same generating capacity. The business of making up lost cycles on a daily business is not easy for utilities. A year or two ago they proposed to let the system float in order to eliminate failures caused by catching up. Fortunately for timenuts, the proposal did not become practice. Bill Hawkins St. Paul: Money is the root of all evil. Ben Franklin: Time is money. Ergo - Time is the root of all evil. -----Original Message----- From: Tom Van Baak Sent: Saturday, November 16, 2013 9:17 PM ---%<--- We measure mains because we can. We also measure it because millions of wall-clocks are based on mains frequency; it was the original "GPSDO". We measure it because its phase plot, frequency histogram, and ADEV plot are really quite interesting. We measure it because Seattle, WA (tvb) and New Mexico (Kevin) are both on the same grid and mutually agree to 10 microseconds (!) over an hour even though they can both wander by many seconds relative to UTC. It's a textbook example of common view time transfer. See also: http://leapsecond.com/pages/mains/ http://leapsecond.com/pages/ac-detect/ You too can join the mains party. Measure it with your own method, or a fancy TrueTime time/frequency deviation meter (TFDM) or use something simple like a picPET (http://www.leapsecond.com/pic/picpet.htm) or Arduino or even a NTP/Linux/serial DCD pin hack. /tvb
TV
Tom Van Baak
Mon, Nov 18, 2013 10:15 PM

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way.

My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab.

/tvb

Magnus, I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot? I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do. Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms. -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor. -- The pink trace was adding a 10 nF cap across the input. -- The green trace was unplugging my laptop switching power supply from the same outlet! -- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way. My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/ My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab. /tvb
BC
Bob Camp
Mon, Nov 18, 2013 10:44 PM

Hi

Let’s hope Santa does not bring you an X10 power line based remote control system for Christmas….

Bob

On Nov 18, 2013, at 5:15 PM, Tom Van Baak tvb@LeapSecond.com wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way.

My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab.

/tvb
<mains-picpet-04.gif>_______________________________________________
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi Let’s hope Santa does not bring you an X10 power line based remote control system for Christmas…. Bob On Nov 18, 2013, at 5:15 PM, Tom Van Baak <tvb@LeapSecond.com> wrote: > Magnus, > > I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot? > > I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do. > > Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms. > > -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor. > -- The pink trace was adding a 10 nF cap across the input. > -- The green trace was unplugging my laptop switching power supply from the same outlet! > -- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way. > > My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/ > > My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab. > > /tvb > <mains-picpet-04.gif>_______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
DJ
Didier Juges
Mon, Nov 18, 2013 10:50 PM

Tom,

Don't confuse everybody with facts, we had a good thread going :)

The PicPet is holding its own very well in that application.

I am surprised at the effect of the laptop supply. I would have certainly expected effect on phase noise (smaller taus), but not that close to the carrier. Do you know if it is a power factor corrected supply or not?

Didier KO4BB

Tom Van Baak tvb@LeapSecond.com wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd
like to see the results of the professional I-Q demodulated gear that
you mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1
Msps is going to reveal interesting amplitude and phase noise
information. But see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is
fast enough to capture the zero-crossing of every 60 Hz cycle with 400
ns resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET
though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from
the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set
to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET
when used this way.

My conclusions are that at least here in the US, or at least at my
house, the short-term stability of mains hits about 5e-6, at about tau
0.2 seconds. The attached short-term plot is also not-inconsistent with
the long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based
time-stamping counter) is doing a pretty good job measuring this. Note,
no software or data filtering was used. This is just raw serial/USB
data going into TimeLab.

/tvb



time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other things.

Tom, Don't confuse everybody with facts, we had a good thread going :) The PicPet is holding its own very well in that application. I am surprised at the effect of the laptop supply. I would have certainly expected effect on phase noise (smaller taus), but not that close to the carrier. Do you know if it is a power factor corrected supply or not? Didier KO4BB Tom Van Baak <tvb@LeapSecond.com> wrote: >Magnus, > >I'm going to push back a bit on your mains sampling claim. Mostly, I'd >like to see the results of the professional I-Q demodulated gear that >you mentioned. Can you post raw data, or a sample plot? > >I agree that looking at power line voltage with 16- or 24-bits at 1 >Msps is going to reveal interesting amplitude and phase noise >information. But see how well a $1 PIC can do. > >Attached is a plot made using TimeLab + picPET just now. The picPET is >fast enough to capture the zero-crossing of every 60 Hz cycle with 400 >ns resolution; the TimeLab plots have tau0 of 16.67 ms. > >-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET >though a 10k resistor. >-- The pink trace was adding a 10 nF cap across the input. >-- The green trace was unplugging my laptop switching power supply from >the same outlet! >-- The red trace is replacing the mains wall-wart with a hp 33120A set >to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET >when used this way. > >My conclusions are that at least here in the US, or at least at my >house, the short-term stability of mains hits about 5e-6, at about tau >0.2 seconds. The attached short-term plot is also not-inconsistent with >the long-term plot at http://leapsecond.com/pages/mains/ > >My other conclusion is that the picPET (a simple PIC-based >time-stamping counter) is doing a pretty good job measuring this. Note, >no software or data filtering was used. This is just raw serial/USB >data going into TimeLab. > >/tvb > > >------------------------------------------------------------------------ > >_______________________________________________ >time-nuts mailing list -- time-nuts@febo.com >To unsubscribe, go to >https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >and follow the instructions there. -- Sent from my Motorola Droid Razr 4G LTE wireless tracker while I do other things.
BD
Bill Dailey
Tue, Nov 19, 2013 1:03 AM

tom,

nice plots.  how do you figure out what the contribution of variability vs
noise? In other words there is a differential between the "ideal" and the
actual a dev curves... is there a way to tease out how much nose contribute
to that differential?  It does seem to me that there should be far less
short term variability (< 100s) than there appears to be.  Clearly in the
very short tau (< 0.1 s) the picPET can't tease that out but as the curves
diverge, how much of that is noise? between say 0.1s and 100s?  Being a
power plant operator I would say quite a bit although I am rethinking that
some due to the way the turbines push and pull each other.  I can envision
some fine whole grid oscillations due to that push and pull.

bill

On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak tvb@leapsecond.com wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd
like to see the results of the professional I-Q demodulated gear that you
mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps
is going to reveal interesting amplitude and phase noise information. But
see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is
fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns
resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET
though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from
the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set to
9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used
this way.

My conclusions are that at least here in the US, or at least at my house,
the short-term stability of mains hits about 5e-6, at about tau 0.2
seconds. The attached short-term plot is also not-inconsistent with the
long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping
counter) is doing a pretty good job measuring this. Note, no software or
data filtering was used. This is just raw serial/USB data going into
TimeLab.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO

tom, nice plots. how do you figure out what the contribution of variability vs noise? In other words there is a differential between the "ideal" and the actual a dev curves... is there a way to tease out how much nose contribute to that differential? It does seem to me that there should be far less short term variability (< 100s) than there appears to be. Clearly in the very short tau (< 0.1 s) the picPET can't tease that out but as the curves diverge, how much of that is noise? between say 0.1s and 100s? Being a power plant operator I would say quite a bit although I am rethinking that some due to the way the turbines push and pull each other. I can envision some fine whole grid oscillations due to that push and pull. bill On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak <tvb@leapsecond.com> wrote: > Magnus, > > I'm going to push back a bit on your mains sampling claim. Mostly, I'd > like to see the results of the professional I-Q demodulated gear that you > mentioned. Can you post raw data, or a sample plot? > > I agree that looking at power line voltage with 16- or 24-bits at 1 Msps > is going to reveal interesting amplitude and phase noise information. But > see how well a $1 PIC can do. > > Attached is a plot made using TimeLab + picPET just now. The picPET is > fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns > resolution; the TimeLab plots have tau0 of 16.67 ms. > > -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET > though a 10k resistor. > -- The pink trace was adding a 10 nF cap across the input. > -- The green trace was unplugging my laptop switching power supply from > the same outlet! > -- The red trace is replacing the mains wall-wart with a hp 33120A set to > 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used > this way. > > My conclusions are that at least here in the US, or at least at my house, > the short-term stability of mains hits about 5e-6, at about tau 0.2 > seconds. The attached short-term plot is also not-inconsistent with the > long-term plot at http://leapsecond.com/pages/mains/ > > My other conclusion is that the picPET (a simple PIC-based time-stamping > counter) is doing a pretty good job measuring this. Note, no software or > data filtering was used. This is just raw serial/USB data going into > TimeLab. > > /tvb > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Doc Bill Dailey KXØO
BC
Bob Camp
Tue, Nov 19, 2013 2:08 AM

Hi

An “ideal” curve would go to the bottom of the scale as soon as the plot started. Anything that shows on the ADEV curve is by definition noise. The slope of the ADEV curve can help you determine what sort of noise it is. The slope(s) on an modified ADEV curve can do that slightly better.

Bob

On Nov 18, 2013, at 8:03 PM, Bill Dailey docdailey@gmail.com wrote:

tom,

nice plots.  how do you figure out what the contribution of variability vs
noise? In other words there is a differential between the "ideal" and the
actual a dev curves... is there a way to tease out how much nose contribute
to that differential?  It does seem to me that there should be far less
short term variability (< 100s) than there appears to be.  Clearly in the
very short tau (< 0.1 s) the picPET can't tease that out but as the curves
diverge, how much of that is noise? between say 0.1s and 100s?  Being a
power plant operator I would say quite a bit although I am rethinking that
some due to the way the turbines push and pull each other.  I can envision
some fine whole grid oscillations due to that push and pull.

bill

On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak tvb@leapsecond.com wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd
like to see the results of the professional I-Q demodulated gear that you
mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps
is going to reveal interesting amplitude and phase noise information. But
see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is
fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns
resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET
though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from
the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set to
9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used
this way.

My conclusions are that at least here in the US, or at least at my house,
the short-term stability of mains hits about 5e-6, at about tau 0.2
seconds. The attached short-term plot is also not-inconsistent with the
long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping
counter) is doing a pretty good job measuring this. Note, no software or
data filtering was used. This is just raw serial/USB data going into
TimeLab.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi An “ideal” curve would go to the bottom of the scale as soon as the plot started. Anything that shows on the ADEV curve is by definition noise. The slope of the ADEV curve can help you determine what sort of noise it is. The slope(s) on an modified ADEV curve can do that slightly better. Bob On Nov 18, 2013, at 8:03 PM, Bill Dailey <docdailey@gmail.com> wrote: > tom, > > nice plots. how do you figure out what the contribution of variability vs > noise? In other words there is a differential between the "ideal" and the > actual a dev curves... is there a way to tease out how much nose contribute > to that differential? It does seem to me that there should be far less > short term variability (< 100s) than there appears to be. Clearly in the > very short tau (< 0.1 s) the picPET can't tease that out but as the curves > diverge, how much of that is noise? between say 0.1s and 100s? Being a > power plant operator I would say quite a bit although I am rethinking that > some due to the way the turbines push and pull each other. I can envision > some fine whole grid oscillations due to that push and pull. > > bill > > > On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak <tvb@leapsecond.com> wrote: > >> Magnus, >> >> I'm going to push back a bit on your mains sampling claim. Mostly, I'd >> like to see the results of the professional I-Q demodulated gear that you >> mentioned. Can you post raw data, or a sample plot? >> >> I agree that looking at power line voltage with 16- or 24-bits at 1 Msps >> is going to reveal interesting amplitude and phase noise information. But >> see how well a $1 PIC can do. >> >> Attached is a plot made using TimeLab + picPET just now. The picPET is >> fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns >> resolution; the TimeLab plots have tau0 of 16.67 ms. >> >> -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET >> though a 10k resistor. >> -- The pink trace was adding a 10 nF cap across the input. >> -- The green trace was unplugging my laptop switching power supply from >> the same outlet! >> -- The red trace is replacing the mains wall-wart with a hp 33120A set to >> 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used >> this way. >> >> My conclusions are that at least here in the US, or at least at my house, >> the short-term stability of mains hits about 5e-6, at about tau 0.2 >> seconds. The attached short-term plot is also not-inconsistent with the >> long-term plot at http://leapsecond.com/pages/mains/ >> >> My other conclusion is that the picPET (a simple PIC-based time-stamping >> counter) is doing a pretty good job measuring this. Note, no software or >> data filtering was used. This is just raw serial/USB data going into >> TimeLab. >> >> /tvb >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > > > > -- > Doc > > Bill Dailey > KXØO > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BD
Bill Dailey
Tue, Nov 19, 2013 2:11 AM

I meant ideal at the noise floor of the picPET (i.e in this case the
generated 60Hz).

On Mon, Nov 18, 2013 at 8:08 PM, Bob Camp lists@rtty.us wrote:

Hi

An “ideal” curve would go to the bottom of the scale as soon as the plot
started. Anything that shows on the ADEV curve is by definition noise. The
slope of the ADEV curve can help you determine what sort of noise it is.
The slope(s) on an modified ADEV curve can do that slightly better.

Bob

On Nov 18, 2013, at 8:03 PM, Bill Dailey docdailey@gmail.com wrote:

tom,

nice plots.  how do you figure out what the contribution of variability

vs

noise? In other words there is a differential between the "ideal" and the
actual a dev curves... is there a way to tease out how much nose

contribute

to that differential?  It does seem to me that there should be far less
short term variability (< 100s) than there appears to be.  Clearly in the
very short tau (< 0.1 s) the picPET can't tease that out but as the

curves

diverge, how much of that is noise? between say 0.1s and 100s?  Being a
power plant operator I would say quite a bit although I am rethinking

that

some due to the way the turbines push and pull each other.  I can

envision

some fine whole grid oscillations due to that push and pull.

bill

On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak tvb@leapsecond.com

wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd
like to see the results of the professional I-Q demodulated gear that

you

mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps
is going to reveal interesting amplitude and phase noise information.

But

see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is
fast enough to capture the zero-crossing of every 60 Hz cycle with 400

ns

resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET
though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from
the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set

to

9VAC at 60 Hz, a tentative noise floor measurement of the picPET when

used

this way.

My conclusions are that at least here in the US, or at least at my

house,

the short-term stability of mains hits about 5e-6, at about tau 0.2
seconds. The attached short-term plot is also not-inconsistent with the
long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping
counter) is doing a pretty good job measuring this. Note, no software or
data filtering was used. This is just raw serial/USB data going into
TimeLab.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO

I meant ideal at the noise floor of the picPET (i.e in this case the generated 60Hz). On Mon, Nov 18, 2013 at 8:08 PM, Bob Camp <lists@rtty.us> wrote: > Hi > > An “ideal” curve would go to the bottom of the scale as soon as the plot > started. Anything that shows on the ADEV curve is by definition noise. The > slope of the ADEV curve can help you determine what sort of noise it is. > The slope(s) on an modified ADEV curve can do that slightly better. > > Bob > > On Nov 18, 2013, at 8:03 PM, Bill Dailey <docdailey@gmail.com> wrote: > > > tom, > > > > nice plots. how do you figure out what the contribution of variability > vs > > noise? In other words there is a differential between the "ideal" and the > > actual a dev curves... is there a way to tease out how much nose > contribute > > to that differential? It does seem to me that there should be far less > > short term variability (< 100s) than there appears to be. Clearly in the > > very short tau (< 0.1 s) the picPET can't tease that out but as the > curves > > diverge, how much of that is noise? between say 0.1s and 100s? Being a > > power plant operator I would say quite a bit although I am rethinking > that > > some due to the way the turbines push and pull each other. I can > envision > > some fine whole grid oscillations due to that push and pull. > > > > bill > > > > > > On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak <tvb@leapsecond.com> > wrote: > > > >> Magnus, > >> > >> I'm going to push back a bit on your mains sampling claim. Mostly, I'd > >> like to see the results of the professional I-Q demodulated gear that > you > >> mentioned. Can you post raw data, or a sample plot? > >> > >> I agree that looking at power line voltage with 16- or 24-bits at 1 Msps > >> is going to reveal interesting amplitude and phase noise information. > But > >> see how well a $1 PIC can do. > >> > >> Attached is a plot made using TimeLab + picPET just now. The picPET is > >> fast enough to capture the zero-crossing of every 60 Hz cycle with 400 > ns > >> resolution; the TimeLab plots have tau0 of 16.67 ms. > >> > >> -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET > >> though a 10k resistor. > >> -- The pink trace was adding a 10 nF cap across the input. > >> -- The green trace was unplugging my laptop switching power supply from > >> the same outlet! > >> -- The red trace is replacing the mains wall-wart with a hp 33120A set > to > >> 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when > used > >> this way. > >> > >> My conclusions are that at least here in the US, or at least at my > house, > >> the short-term stability of mains hits about 5e-6, at about tau 0.2 > >> seconds. The attached short-term plot is also not-inconsistent with the > >> long-term plot at http://leapsecond.com/pages/mains/ > >> > >> My other conclusion is that the picPET (a simple PIC-based time-stamping > >> counter) is doing a pretty good job measuring this. Note, no software or > >> data filtering was used. This is just raw serial/USB data going into > >> TimeLab. > >> > >> /tvb > >> > >> _______________________________________________ > >> time-nuts mailing list -- time-nuts@febo.com > >> To unsubscribe, go to > >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > >> and follow the instructions there. > >> > > > > > > > > -- > > Doc > > > > Bill Dailey > > KXØO > > _______________________________________________ > > time-nuts mailing list -- time-nuts@febo.com > > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > > and follow the instructions there. > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. > -- Doc Bill Dailey KXØO
PG
Peter Gottlieb
Tue, Nov 19, 2013 2:35 AM

The power supply contribution is interesting.  This might have been a useful
tool when a year ago I was playing with some very large inverters on a
microgrid.  I had one inverter as master (in UF mode) and two others as
grid-connected slaves in PQ mode.  The first slave would come online just fine
yet when the second was synched the entire microgrid would go unstable.  It was
noise at the zero crossings but not enough to see on a scope.

With all the distributed generation coming online I would be wary of relying on
those zero crossings.

Peter

On 11/18/2013 5:15 PM, Tom Van Baak wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way.

My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

The power supply contribution is interesting. This might have been a useful tool when a year ago I was playing with some very large inverters on a microgrid. I had one inverter as master (in UF mode) and two others as grid-connected slaves in PQ mode. The first slave would come online just fine yet when the second was synched the entire microgrid would go unstable. It was noise at the zero crossings but not enough to see on a scope. With all the distributed generation coming online I would be wary of relying on those zero crossings. Peter On 11/18/2013 5:15 PM, Tom Van Baak wrote: > Magnus, > > I'm going to push back a bit on your mains sampling claim. Mostly, I'd like to see the results of the professional I-Q demodulated gear that you mentioned. Can you post raw data, or a sample plot? > > I agree that looking at power line voltage with 16- or 24-bits at 1 Msps is going to reveal interesting amplitude and phase noise information. But see how well a $1 PIC can do. > > Attached is a plot made using TimeLab + picPET just now. The picPET is fast enough to capture the zero-crossing of every 60 Hz cycle with 400 ns resolution; the TimeLab plots have tau0 of 16.67 ms. > > -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET though a 10k resistor. > -- The pink trace was adding a 10 nF cap across the input. > -- The green trace was unplugging my laptop switching power supply from the same outlet! > -- The red trace is replacing the mains wall-wart with a hp 33120A set to 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when used this way. > > My conclusions are that at least here in the US, or at least at my house, the short-term stability of mains hits about 5e-6, at about tau 0.2 seconds. The attached short-term plot is also not-inconsistent with the long-term plot at http://leapsecond.com/pages/mains/ > > My other conclusion is that the picPET (a simple PIC-based time-stamping counter) is doing a pretty good job measuring this. Note, no software or data filtering was used. This is just raw serial/USB data going into TimeLab. > > /tvb > > > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
BC
Bob Camp
Tue, Nov 19, 2013 2:36 AM

Hi

There is no way to come up with the noise floor of the picPET from that plot. In fact coming up with the floor of a single channel device like the picPET is not all that easy. First you need an ideal noise free sine wave signal …. I’ve spent more than a few hours on that particular project with other list members involved as well. As always we kept it off list to keep from offending those who place a high value on their bandwidth.

Bob

On Nov 18, 2013, at 9:11 PM, Bill Dailey docdailey@gmail.com wrote:

I meant ideal at the noise floor of the picPET (i.e in this case the
generated 60Hz).

On Mon, Nov 18, 2013 at 8:08 PM, Bob Camp lists@rtty.us wrote:

Hi

An “ideal” curve would go to the bottom of the scale as soon as the plot
started. Anything that shows on the ADEV curve is by definition noise. The
slope of the ADEV curve can help you determine what sort of noise it is.
The slope(s) on an modified ADEV curve can do that slightly better.

Bob

On Nov 18, 2013, at 8:03 PM, Bill Dailey docdailey@gmail.com wrote:

tom,

nice plots.  how do you figure out what the contribution of variability

vs

noise? In other words there is a differential between the "ideal" and the
actual a dev curves... is there a way to tease out how much nose

contribute

to that differential?  It does seem to me that there should be far less
short term variability (< 100s) than there appears to be.  Clearly in the
very short tau (< 0.1 s) the picPET can't tease that out but as the

curves

diverge, how much of that is noise? between say 0.1s and 100s?  Being a
power plant operator I would say quite a bit although I am rethinking

that

some due to the way the turbines push and pull each other.  I can

envision

some fine whole grid oscillations due to that push and pull.

bill

On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak tvb@leapsecond.com

wrote:

Magnus,

I'm going to push back a bit on your mains sampling claim. Mostly, I'd
like to see the results of the professional I-Q demodulated gear that

you

mentioned. Can you post raw data, or a sample plot?

I agree that looking at power line voltage with 16- or 24-bits at 1 Msps
is going to reveal interesting amplitude and phase noise information.

But

see how well a $1 PIC can do.

Attached is a plot made using TimeLab + picPET just now. The picPET is
fast enough to capture the zero-crossing of every 60 Hz cycle with 400

ns

resolution; the TimeLab plots have tau0 of 16.67 ms.

-- The blue trace was simply plugging a 9 VAC wall-wart into the picPET
though a 10k resistor.
-- The pink trace was adding a 10 nF cap across the input.
-- The green trace was unplugging my laptop switching power supply from
the same outlet!
-- The red trace is replacing the mains wall-wart with a hp 33120A set

to

9VAC at 60 Hz, a tentative noise floor measurement of the picPET when

used

this way.

My conclusions are that at least here in the US, or at least at my

house,

the short-term stability of mains hits about 5e-6, at about tau 0.2
seconds. The attached short-term plot is also not-inconsistent with the
long-term plot at http://leapsecond.com/pages/mains/

My other conclusion is that the picPET (a simple PIC-based time-stamping
counter) is doing a pretty good job measuring this. Note, no software or
data filtering was used. This is just raw serial/USB data going into
TimeLab.

/tvb


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Doc

Bill Dailey
KXØO


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi There is no way to come up with the noise floor of the picPET from that plot. In fact coming up with the floor of a single channel device like the picPET is not all that easy. First you need an ideal noise free sine wave signal …. I’ve spent more than a few hours on that particular project with other list members involved as well. As always we kept it off list to keep from offending those who place a high value on their bandwidth. Bob On Nov 18, 2013, at 9:11 PM, Bill Dailey <docdailey@gmail.com> wrote: > I meant ideal at the noise floor of the picPET (i.e in this case the > generated 60Hz). > > > On Mon, Nov 18, 2013 at 8:08 PM, Bob Camp <lists@rtty.us> wrote: > >> Hi >> >> An “ideal” curve would go to the bottom of the scale as soon as the plot >> started. Anything that shows on the ADEV curve is by definition noise. The >> slope of the ADEV curve can help you determine what sort of noise it is. >> The slope(s) on an modified ADEV curve can do that slightly better. >> >> Bob >> >> On Nov 18, 2013, at 8:03 PM, Bill Dailey <docdailey@gmail.com> wrote: >> >>> tom, >>> >>> nice plots. how do you figure out what the contribution of variability >> vs >>> noise? In other words there is a differential between the "ideal" and the >>> actual a dev curves... is there a way to tease out how much nose >> contribute >>> to that differential? It does seem to me that there should be far less >>> short term variability (< 100s) than there appears to be. Clearly in the >>> very short tau (< 0.1 s) the picPET can't tease that out but as the >> curves >>> diverge, how much of that is noise? between say 0.1s and 100s? Being a >>> power plant operator I would say quite a bit although I am rethinking >> that >>> some due to the way the turbines push and pull each other. I can >> envision >>> some fine whole grid oscillations due to that push and pull. >>> >>> bill >>> >>> >>> On Mon, Nov 18, 2013 at 4:15 PM, Tom Van Baak <tvb@leapsecond.com> >> wrote: >>> >>>> Magnus, >>>> >>>> I'm going to push back a bit on your mains sampling claim. Mostly, I'd >>>> like to see the results of the professional I-Q demodulated gear that >> you >>>> mentioned. Can you post raw data, or a sample plot? >>>> >>>> I agree that looking at power line voltage with 16- or 24-bits at 1 Msps >>>> is going to reveal interesting amplitude and phase noise information. >> But >>>> see how well a $1 PIC can do. >>>> >>>> Attached is a plot made using TimeLab + picPET just now. The picPET is >>>> fast enough to capture the zero-crossing of every 60 Hz cycle with 400 >> ns >>>> resolution; the TimeLab plots have tau0 of 16.67 ms. >>>> >>>> -- The blue trace was simply plugging a 9 VAC wall-wart into the picPET >>>> though a 10k resistor. >>>> -- The pink trace was adding a 10 nF cap across the input. >>>> -- The green trace was unplugging my laptop switching power supply from >>>> the same outlet! >>>> -- The red trace is replacing the mains wall-wart with a hp 33120A set >> to >>>> 9VAC at 60 Hz, a tentative noise floor measurement of the picPET when >> used >>>> this way. >>>> >>>> My conclusions are that at least here in the US, or at least at my >> house, >>>> the short-term stability of mains hits about 5e-6, at about tau 0.2 >>>> seconds. The attached short-term plot is also not-inconsistent with the >>>> long-term plot at http://leapsecond.com/pages/mains/ >>>> >>>> My other conclusion is that the picPET (a simple PIC-based time-stamping >>>> counter) is doing a pretty good job measuring this. Note, no software or >>>> data filtering was used. This is just raw serial/USB data going into >>>> TimeLab. >>>> >>>> /tvb >>>> >>>> _______________________________________________ >>>> time-nuts mailing list -- time-nuts@febo.com >>>> To unsubscribe, go to >>>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>>> and follow the instructions there. >>>> >>> >>> >>> >>> -- >>> Doc >>> >>> Bill Dailey >>> KXØO >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. >> > > > > -- > Doc > > Bill Dailey > KXØO > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.